07-12-2010, 11:39 AM #1
Hydrocarbon venting
Hi all
Not sure if this is just news to me but venting refrigerants is illegal, unless we are talking hydrocarbon 'natural refrigerants'
Current practice in the UK (in line with Europe) is to vent up to 150g of HC refrigerant when servicing systems.
This would apply to commercial cabinets that do not exceed 150g.
The HC must be vented to outside a building, at least 2 m from the building where the air is moving to disperse the refrigerant safely, away from sources of ignition and where it will not drop into below ground areas.
Lifes for learning.
-
07-12-2010, 02:02 PM #2
Re: Hydrocarbon venting
Venting hydrocarbons is not illegal, up to now.
Actually, PE foams are expanded with HC gases, mainly isobutane. After the expansion, HC is replaced with air in special curing warehouses.
It is good practice, though,to properly avoid accumulation, as you mentioned.
-
08-12-2010, 09:52 AM #3
Re: Hydrocarbon venting
Hi NoNickName
Your absolutely right.
Cyclopentane is another natural hydrocarbon gas used as a foam propellant.
I know some manufacturers still use 134a in the commercial cabinet sector.
Similar Threads
-
Hydrocarbon in R134a system.... 1/3 Charge and 1/2 Charge of R134a?
By Z2TT in forum RefrigerantsReplies: 6Last Post: 08-11-2010, 01:56 AM -
Freeze Spray -- Venting R134a Illegal?
By Z2TT in forum Chit Chat & Service StoriesReplies: 10Last Post: 29-07-2010, 09:29 PM -
COMPARISON OF HYDROCARBON R-290 AND
By shogun7 in forum RefrigerantsReplies: 17Last Post: 12-01-2009, 07:30 PM -
Illegal venting of refrigerants
By chataroets in forum RefrigerantsReplies: 10Last Post: 22-01-2008, 07:02 PM -
Hydrocarbon refrigerants
By mbeychok in forum RefrigerantsReplies: 15Last Post: 01-09-2006, 10:03 PM