    elliwell ID974 defrost problems



    We have a kitchen deepfreezer onboard controlled by an elliwell ID974.
    We cleaned it out and manually defrosted it and when we started it up again the compressor started running but the fan did not, so the temperature in the freezer didn't come down.
    When I disabled the evaporator probe by changing the parameter H42 to 'no' the fan started running and the temperature started coming down.
    When it reached normal working temperatures again, I changed the parameter back to 'yes' and the fan kept on turning and everything kept on working fine.
    But a few hours later it went in defrost and the letters 'def' appeared in the display and stayed there.
    The temperature stayed ok but the only way to get rid of the 'def' was by switching the refrigerator off and on again.
    Does anybody have an idea what could be the reason of this phenomena.
    Thanks
    Danny
    Last edited by boksida@hotmail; 21-09-2007 at 04:00 PM.



  2. #2
    Join Date
    Jan 2006
    Location
    UK
    Posts
    53
    Rep Power
    19

    Re: elliwell ID974 defrost problems

    The Eliwell ID974 has some 40 instructions; it’s easy to get lost, frustrated and generally fed-up when it doesn't appear to work!

    There are two instruction FSt & FAd which together will hold off the fan until the coil reaches a certain temperature. If say, FSt was set for 5°C and FAd was set for 2°C, the fans will come on when the coil temperature reaches
    5 – 2 = 3°C.

    Another instruction FCO, will cycle the fans with the compressor during cooling.

    The display in defrost is controlled by instruction ddL.

    If ddL is set for “2” then the display will show deF when the defrost starts and continue to show deF until the air falls below the setpoint temperature.

    Full instructions for ID974 and other controllers here: http://www.frostechnic.com/service.htm

    Hope this helps.
    Last edited by walden; 21-09-2007 at 04:34 PM. Reason: grammar!

  3. #3
    Join Date
    Sep 2007
    Location
    Italy
    Posts
    15
    Rep Power
    0

    Re: elliwell ID974 defrost problems

    Sirs,

    you can download all eliwell literature on Invensyscontrolsuerope.com website under Eliwell brand. Refrigeration controllers like ID974 are under digifrost controller. For any help you can contact
    techsuppeliwell@invensyscontrols.com

    regards

  4. #4
    cuepower64's Avatar
    cuepower64 Guest

    Re: elliwell ID974 defrost problems

    The ID974 DEF display will keep displaying until the controller setpoint is reached. As for the fans I would check that the fan off temperature parameter is not set too low, as if this is set too low the fans will not energise until the temperature drops back down to this setting due to the temperature rise on defrost. Also I dare say you have checked this but also check the fan delay time as both of these will hold the fan off after a defrost. I hope this helps!!! cuepower64
    Quote Originally Posted by boksida@hotmail View Post
    We have a kitchen deepfreezer onboard controlled by an elliwell ID974.
    We cleaned it out and manually defrosted it and when we started it up again the compressor started running but the fan did not, so the temperature in the freezer didn't come down.
    When I disabled the evaporator probe by changing the parameter H42 to 'no' the fan started running and the temperature started coming down.
    When it reached normal working temperatures again, I changed the parameter back to 'yes' and the fan kept on turning and everything kept on working fine.
    But a few hours later it went in defrost and the letters 'def' appeared in the display and stayed there.
    The temperature stayed ok but the only way to get rid of the 'def' was by switching the refrigerator off and on again.
    Does anybody have an idea what could be the reason of this phenomena.
    Thanks
    Danny

  5. #5
    Join Date
    Oct 2007
    Location
    Belgrade
    Age
    47
    Posts
    10
    Rep Power
    0

    Re: elliwell ID974 defrost problems

    There is another thing that could hold the fans. Dripping time (dT) It is used to hold fans until remaining water drops turns into ice so they cant be blown off of the evap.
    Check that, too.

  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Thumbs up Re: elliwell ID974 defrost problems

    Boksida.
    I think the link you recieved from mambro 01 is corrupted.
    Please follow the link below for the relevant pdf for the ellwel ID Range including the manual for a ID974 and a ID974LX. The instruction manual link is at the bottom of the page.
    Grizzly
    http://www.invensyscontrolseurope.co...DigifrostLine/

  7. #7
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: elliwell ID974 defrost problems

    boksida,

    could you check on your temperature sensor probe/s?
    you should find somthing there.

  8. #8
    Join Date
    Dec 2007
    Location
    Devon
    Age
    73
    Posts
    8
    Rep Power
    0

    Re: elliwell ID974 defrost problems

    I agree with hendry, had same problem, changed the evap probe. All OK (Prefer LAE )

  9. #9
    Join Date
    Dec 2007
    Location
    Volos, Greece
    Posts
    46
    Rep Power
    0

    Re: elliwell ID974 defrost problems

    I Had many times the same problems , sometimes the def probe can stop the fans and can be damaged without probe alarm,

  10. #10
    Join Date
    Dec 2007
    Location
    malaysia
    Posts
    159
    Rep Power
    17

    Re: elliwell ID974 defrost problems

    Quote Originally Posted by Mazdamike View Post
    I agree with hendry, had same problem, changed the evap probe. All OK (Prefer LAE )
    thank you for your concurrence.

    sometimes, i need to be a bit more adventurous in order to complete the entrusted task/job.

    no doubt, it may seem to be a simple alarm ...

    i do check the complete electrical and electronic system to eliminate any nuisance.

    anyway, good luck in case you have similar problem/s.

    BEAR IN MIND NOT ANY TWO PROBLEMS ARE THE SAME.

  11. #11
    Join Date
    Feb 2008
    Location
    stevenage england chav central
    Age
    51
    Posts
    44
    Rep Power
    0

    Re: elliwell ID974 defrost problems

    hello well to start off these controllers are easy once you get to know the patterns and the things you need to look for as someone said check the evp probe and temperature reading within the controller i am sure it is a function on this controller then check and make sure the probe is attached to the evp that could be another problem sometimes they fall off or get disloged, check evp cut in time sometimes its on a time basis or a temp basis depending on the settings within the controller and last of all check the gas charge maybe there is not enough refrigerant flooding the evp to insure that the fan comes on within the set parameters i hope this helps.
    declan

  12. #12
    armyeng1's Avatar
    armyeng1 Guest

    Re: elliwell ID974 defrost problems

    I have an elliwell ID974 Controller with LED display showing the compressor off, but the compressor continues to cool anyways and the fan does not stop. I have the SET to 2C and the Dif to 2C everything appears ok, both NTC probes are new. Any ideas?

  13. #13
    Join Date
    Dec 2009
    Location
    dublin
    Posts
    14
    Rep Power
    0

    Re: elliwell ID974 defrost problems

    if u have a solenid check to see if its passing,if there is no solenid check if your controller is still sending power to compressor when its not calling 4 it

  14. #14
    Join Date
    Oct 2008
    Location
    New Zealand
    Age
    46
    Posts
    33
    Rep Power
    0

    Re: elliwell ID974 defrost problems

    Quote Originally Posted by armyeng1 View Post
    I have an elliwell ID974 Controller with LED display showing the compressor off, but the compressor continues to cool anyways and the fan does not stop. I have the SET to 2C and the Dif to 2C everything appears ok, both NTC probes are new. Any ideas?
    relay locked on. replace controller.

  15. #15
    Join Date
    Jan 2006
    Location
    Adelaide , Australia
    Posts
    192
    Rep Power
    19

    Re: elliwell ID974 defrost problems

    How do I put Elliwell ID974 - onto defrost ?
    60% of the time it works everytime.

  16. #16
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: elliwell ID974 defrost problems

    hit the bugger timbo
    mmm to beer or not to beer...........lets drink breakfast

  17. #17
    Join Date
    May 2005
    Location
    newbury
    Age
    43
    Posts
    13
    Rep Power
    0

    Re: elliwell ID974 defrost problems

    Hold down top left button to defrost

  18. #18
    Join Date
    Jan 2006
    Location
    Adelaide , Australia
    Posts
    192
    Rep Power
    19

    Re: elliwell ID974 defrost problems

    Quote Originally Posted by lowcool View Post
    hit the bugger timbo


    PDF arrived from Elliwell tech support impressive it has all the info , but i dont know how to attach it ?
    Last edited by Toolman; 17-12-2010 at 08:48 AM.
    60% of the time it works everytime.

  19. #19
    Join Date
    Jan 2006
    Location
    Adelaide , Australia
    Posts
    192
    Rep Power
    19

    Talking Re: elliwell ID974 defrost problems

    Quote Originally Posted by mambro_01 View Post
    Sirs,

    you can download all eliwell literature on Invensyscontrolsuerope.com website under Eliwell brand. Refrigeration controllers like ID974 are under digifrost controller. For any help you can contact
    techsuppeliwell@invensyscontrols.com

    regards
    Thanks for the email address they sent me exactly what I needed in a PDF
    60% of the time it works everytime.

Similar Threads

  1. Elliwell digital controller
    By chenkang in forum Electrical
    Replies: 12
    Last Post: 25-09-2009, 11:36 AM
  2. Hot gas defrost vs Electric defrost
    By herdian in forum Industrial
    Replies: 19
    Last Post: 13-08-2007, 11:25 PM
  3. Freezer Room Defrost
    By Samarjit Sen in forum Commissioning
    Replies: 23
    Last Post: 21-06-2007, 06:16 AM
  4. Hot Gas vs. Electric Defrost
    By herefishy in forum Technical Discussions
    Replies: 26
    Last Post: 08-03-2005, 07:50 PM
  5. Oil return problems
    By Peter_1 in forum Industrial
    Replies: 37
    Last Post: 23-08-2004, 11:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •