11-12-2010, 01:23 PM #1
How do I charge R 407
Hi all .... I still do not understand how charging R407 in cooling system does indeed have to enter the liquid from the suction line?
Thanks ........
-
11-12-2010, 01:30 PM #2
Re: How do I charge R 407
Yes, and the best place is before the accumulator.
-
11-12-2010, 01:52 PM #3
Re: How do I charge R 407
The refrigerant must be drawn from the cylinder as a liquid.
Once it is removed from the cylinder, it's fine if it evaporates.
Some manufacturers make an orifice that fits into your charging hoses to flash the liquid off before it enters the system.
-
11-12-2010, 03:02 PM #4
Re: How do I charge R 407
It is better to charge liquid R407 in liquid line (receiver), when compressor is stopped. When needed, refrigerant may be added in the liquid phase, carefully throttling the refrigerant on the low-pressure side and as far as possible from compressor. The compressor must be operating during this process.
-
11-12-2010, 03:05 PM #5
Re: How do I charge R 407
hi Eep,
I take it you are charging from a vaced out system? so you have pressure tested . and veced out ? place your gas bottle on your weighing scales and charge the liquid into the recever< condencer< to the correct weight ,
if its a water chiller, or /and a water cooled unit all water pumps must be running. sedgy,
-
14-12-2010, 05:24 AM #6
Re: How do I charge R 407
OK Thank's to all................
-
17-12-2010, 06:03 PM #7
Re: How do I charge R 407
hi
you can charge it by throtteling way thats mean open and close
-
17-12-2010, 09:33 PM #8
Re: How do I charge R 407
r407c can only be charged as a liquid and in a liquid port.if system has a refrig shortage then all the remaining gas must be recovered and be recharged with liquid only.
-
18-12-2010, 04:57 PM #9
Re: How do I charge R 407
Sorry Jimmy
What you are quoting is not std practise nowadays.
It has become quite acceptable to add fresh to what is a part charged system.
I know there is the argument about fictionalisation (splitting) of the refrigerant.
But experience has shown that total recovery and recharge with new is not always necessary or practical.
I would say it all depends upon the size of the plant.
There is nothing stopping a system being charged on the LP side.
Provided it leaves the cylinder as liquid and and enters the system as saturated vapour.
This can be achieved by throttling the valves across your manifold.
You do indeed need to be cautious about the amounts metered into the lp but it is a good way of finally trimming the system charge whilst running.
Although size of plant would again dictate.
Grizzly
-
18-12-2010, 05:07 PM #10
Re: How do I charge R 407
The larger the system the less likely your added charge, which has the correct component proportions, is able to blanket the effect of any fractionation caused by a leak.
Leaks toward the end of the evaporator and toward the beginning of the condenser will cause greatest degrees of charge fractionation.Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.
-
18-12-2010, 07:31 PM #11
Re: How do I charge R 407
I could not agree more.
Where the leak occurs has great relevance as do many factors!
To be precise quoting the institute of refrigeration's
own service papers.
Zeotropic refrigerants can be added to a part charged system and it will work.
Except where a system is critically charged.
All i wanted to point out was that jimmy's statement was no longer entirely correct.
It is however one that a lot of people quote.
Grizzly.
-
18-12-2010, 09:00 PM #12
Re: How do I charge R 407
Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.
-
18-12-2010, 09:50 PM #13
Re: How do I charge R 407
Similar Threads
-
Hydrocarbon in R134a system.... 1/3 Charge and 1/2 Charge of R134a?
By Z2TT in forum RefrigerantsReplies: 6Last Post: 08-11-2010, 01:56 AM -
split inverter unsure of proper charge spec.. how to charge?
By cadillackid in forum Air ConditioningReplies: 4Last Post: 19-11-2009, 01:52 PM -
first estimate of system charge
By cool-hvacer in forum FundamentalsReplies: 25Last Post: 03-02-2009, 10:34 AM -
Subcooling vs charge graph?
By Larry2 in forum FundamentalsReplies: 4Last Post: 01-12-2006, 07:40 PM -
Who's in charge?
By chillin out in forum Chit Chat & Service StoriesReplies: 1Last Post: 01-10-2006, 10:51 PM