    Mitsubishi problem



    Hi All,

    We have a large multi-city install with 3 x 2 banks of units on the roof, about 90 internal units split over 50 offices and 3 floors controlled via 3 x g50 controllers.

    We currently have no heating and can not get hold of out engineers!

    The local controllers in the offices are giving a variety of codes including 7100 and 7102. The G50's are showing no errors!

    Can someone point me in the right direction to get things running again?

    Thanks.



  2. #2
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Mitsubishi problem

    Hey Matt
    7100 ,7101,7102 are all capacity errors, meaning the outdoor units detect either too many indoor units connected or no indoor units connected, a power reset at the outdoor unit usually clears this up providing you have power at all indoors and bc's . If not check transmission line voltage and capacity setting setting on outdoor board sw2 if memory serves me correctlly.. best of luck !!

    Stu

  3. #3
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Mitsubishi problem

    Matt its actually SW3-10 for outdoor unit capacity.
    SW2 is capacity for the indoor units and is listed on the indoor electrical cover.selector
    switch (SW3-10).
    1) The Indoor unit model name (model
    code) connected is not connectable.
    Connectable range.....20~250
    2) Erroneous setting of the switch
    (SW2) for setting of model name of
    Indoor unit connected.
    1) Number of unit connected to terminal
    block (TB3) for outdoor/indoor
    transmission line exceeds limitations
    given be-lows:
    Item Limitation
    Total of 200:1~13
    Indoor unit 250:1~16
    Total of Indoor
    unit & RC 1~35
    (3) System error
    Checking
    code
    7100
    7101
    7102
    Meaning, detecting method Cause Checking method & Countermeasure
    Total capacity error
    Total capacity of indoor units in
    the same refrigerant system exceeds
    limitations.
    Trouble source:
    Outdoor unit
    Capacity code error
    Error display at erroneous connection
    of Indoor unit of which
    model name can not be connected.
    Trouble source :
    Outdoor unit
    Indoor unit
    Connected unit count over
    Number of units connected in the
    same refrigerant system exceeds
    limitations.
    Trouble source:
    Outdoor unit
    a) Check for the model total (capacity cord total) of
    indoor units connected.
    b) Check whether indoor unit capacity code (SW2)
    is wrongly set.
    For erroneous switch setting, modify it, turn off
    power source of outdoor unit, and indoor unit
    simultaneously for 5 minutes or more to modify
    the switch for setting the model name (capacity
    coad).
    Check for the model selector switch (Dip switches
    SW3-10 on outdoor unit control circuit) of OC.
    a) Check for the model name of the Indoor unit
    connected.
    b) Check for the switch (SW2 if indoor controller
    for setting of Indoor unit model name of generating
    address. When it is not agreed to the model
    name, modify the capacity code while shutting
    off the power source of Indoor unit.
    ❇ The capacity of Indoor unit can be confirmed by
    the self-diagnosios function (SW1 operation) of
    Indoor unit.
    a) Check whether the connection of units to the
    terminal block for indoor/outdoor transmission
    wiring (TB3) of outdoor unit is not exceeding the
    limitation.
    b) Check for 2), 3), and 4).
    c) Check for the connection of transmission wiring
    to the terminal block for centralized control is
    erroneously connected to the indoor/outdoor
    transmission wiring terminal block (TB3).
    Model Total capacity code
    200 53
    250 66
    1
    ON 250
    OFF 200
    2 3 4 5
    SW3
    6 7 8 9 10
    .....

  4. #4
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Mitsubishi problem

    1st Try a re set by going to each G50 & switch off all indoor units.
    Then switch all indoor units back on.

    If problems continue
    Carry out a full system reset. For this you need to turn off electrical power to all indoor units & outdoor units.
    1/ Turn off all indoor units at the G50 central controllers.
    2/ Find the power distribution board which serves the outdoor units & turn off the 3 phase power to all the outdoor units.
    3/ Find the power distribution board on each floor & turn off the ring main circuits to all the indoor units. Leave switched off for a few mins & then turn back on.
    4/ Go back & turn on the 3 phase power to all the indoor units.
    5/ After 5 mins go to each G50 & turn all indoor units back on.

    If the faults are only with one system & G50 then only do the full power reset to that G50 & indoor units / outdoor unit on that floor.

    If your building is very cold inside it may take quite a few hours to gradually warm up even with all systems fully operational & outdoor units running flat out.
    With this extreem cold weather I would recomend leave to operate 24/7 untill the cold weather passes.

    Any further problem will need the maintenance contractor to attend site & investigate.
    Most contractors are flat out busy due to the extreem weather at the moment.

  5. #5
    mattltm's Avatar
    mattltm Guest

    Re: Mitsubishi problem

    Thanks all for your advice and help.

    The fault turned out to be a dead unit on the roof. We replaced the noise filter PCB and all is now working fine.

    Thanks for the help.

  6. #6
    Join Date
    Mar 2011
    Location
    Singapore
    Posts
    212
    Rep Power
    16

    Re: Mitsubishi problem

    Thanks mattltm, in general noise filter cases are belong to error codes 4xxx but your case is 7xxx.
    Stufus's approach is better because we normally 7xxx are more relate to either capactiy or Mnet.
    However we noted your resolution.

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi problem

    4 1/2 months to rectify-not bad

  8. #8
    Join Date
    Mar 2011
    Location
    Singapore
    Posts
    212
    Rep Power
    16

    Re: Mitsubishi problem

    Quote Originally Posted by install monkey View Post
    4 1/2 months to rectify-not bad
    Don't worried RE forum is active, he could be here sooner, most worse cases 4 1/2 days or some 4 1/2 hrs I beleived. Don't you agree?? Hey Stufus, support me...

  9. #9
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Mitsubishi problem

    All's well that ends well .
    Better late than never
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

Similar Threads

  1. Mitsubishi City Multi Heating Problem
    By Contactor in forum Air Conditioning
    Replies: 1
    Last Post: 27-11-2010, 10:07 PM
  2. Mitsubishi G50 / City Multi Control Problem
    By Contactor in forum Air Conditioning
    Replies: 3
    Last Post: 12-11-2010, 08:00 PM
  3. A strange problem
    By MuhengineeR in forum Air Conditioning
    Replies: 14
    Last Post: 27-10-2010, 05:21 PM
  4. Please Help Mitsubishi Heavy Ind problem
    By simplycooling in forum Air Conditioning
    Replies: 23
    Last Post: 02-03-2009, 11:18 PM
  5. Furance problem
    By ALONEI in forum Trouble Shooting
    Replies: 10
    Last Post: 14-05-2008, 11:32 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •