    Hi guys, I've been working on a large packaged heat pump unit and I noticed the supply air was between 15-20C which is too low.
    The bottom of the evaporator was heavily iced.

    On the evaporator is a defrost stat that was fitted by the original installers at a later date.
    The defrost stat has a bulb that sits in-between the coil and switches the 4way rv when ever it senses the set temp.

    However I'm unsure as to what it should be set at.
    It was originally set at 0C but if I leave it at that setting then the unit constantly goes on defrost (every 5 mins or so)
    Could this defrost method work without a timer or is there something I'm missing.


    The difference between genius and stupidity is that genius has its limits.

    Marc

  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Defrost stat

    hi marc,
    what % of fresh air have you got ? and whats the ambiant ?

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Defrost stat

    I'm not sure what percentage the fresh air is to the coil as it goes through a recouperator that looks like it mixes with the return air from the building.
    I'm going to try to speak to the manufacturers tomorrow regarding this.

    The ambient temp is -1C.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  4. #4
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Defrost stat

    hi marc,
    well in this weather I would shut down all external air, what is the axilary heating?

  5. #5
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: Defrost stat

    Does the fan shut off whilst its defrosting? Maybe set the defrost stat to 10 deg C as a starting point, then monitor the ambience over 15 minute intervals. Defrost intervals for any fridge or aircon system, have different taylored parameters for each system. But I know that you already know that.

  6. #6
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Defrost stat

    I dont think its's an option to shut off all the external air although i will try this when i go back. I think this may cause lack of airflow across the coil maybe i'm wrong but i'll check this.

    The auxillary heating is by an electric heater just after the fresh air inlet ( this was on 100%)
    The difference between genius and stupidity is that genius has its limits.

    Marc

  7. #7
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Defrost stat

    Quote Originally Posted by chilliwilly View Post
    Does the fan shut off whilst its defrosting? Maybe set the defrost stat to 10 deg C as a starting point, then monitor the ambience over 15 minute intervals. Defrost intervals for any fridge or aircon system, have different taylored parameters for each system. But I know that you already know that.
    No the fan doesn't shut off. As this is an after market frost stat fitted it is very basic and the control logic is as simple as when it senses the bulb temp is at the stat set temp then it switches the 4way rv.

    It doesn't use a timer, ambient temperature sensor or even switch the fan off to control the defrost.
    The difference between genius and stupidity is that genius has its limits.

    Marc

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. maytag fridge activation of new controller
    By jdrefrigeration in forum Domestic
    Replies: 5
    Last Post: 09-03-2010, 12:00 PM
  3. Toshiba RAV SM/SP1400 defrost problem
    By SteinarN in forum Heat Pumps
    Replies: 11
    Last Post: 20-02-2008, 04:25 PM
  4. No Power for Defrost Timer Motor
    By kln in forum Domestic
    Replies: 6
    Last Post: 21-01-2008, 08:22 AM
  5. Best place for defrost termination stat
    By Contactor in forum Fundamentals
    Replies: 3
    Last Post: 06-06-2007, 04:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •