im working on a newly installed -23 degrees freezer room 100% back up system 1 is working perfect put the back up system solnoid will not close fully and only somtimes open.im on my third solnoid vavle but still no luck has ne one ever come across this?
-
02-12-2010, 02:05 AM #2
Re: Going mad
Look for induced voltages that will hold sv open. Then crunch coils.
Plus where is sligo on the world map
-
02-12-2010, 10:15 PM #3
Re: Going mad
Will it open and close fully with a magnet? If it does replace coil and check voltages, check coil is correct for voltage applied.
Unusual to have a solenoid fail so soon, if not above then you've ****e in the valve holding it open.
alec
-
02-12-2010, 10:35 PM #4
Re: Going mad
What type of controller is feeding the solenoid, check that the controller is not set for an eev, as this maybe why it dosent shut down for a prolonged period.
Supermarketguy
-
03-12-2010, 11:21 AM #5
Re: Going mad
Magoo,
Sligo is a large town in the County of Sligo, North west Ireland. I have found memories of that town as that were I started my fridge career, and had many, many, many a good night out in that town, and many, many, many hangovers too!
-
03-12-2010, 12:08 PM #6
Re: Going mad
.
The other thing to look at is the type of coil.
Make sure it is the correct one and not a coil for an expansion valve.
They look the same but have different AC / DC rateings.
All the best
taz
.
-
10-01-2011, 11:08 PM #7
Re: Going mad
Thanks for all the suggestions ended up throwing out the alco solonoid vavles and used Danfoss instead problem was sorted cheers
-
11-01-2011, 07:51 PM #8