Denco D28AVH
Hi Chaps,
Does anyone have a pipe size chart for R407c refrigerant, coz i have a Denco unit which was commissioned back in 2008 with 25kg of refrigerant. i think this is wrong as the gauges tell me a different story. I've checked the pipe run and it is 128meters roughly from indoor to oudoor and back again. The pipe size is 1" 7/8 and 5/8" i have just reclaimed 24kg. Pressure tested and vacced and re-charged with 32kg, i bomb charged the system till i had a full sight glass and then trim charged. The problem is i am only getting 14bar discharge pressure and 3.5bar SUCTION pressure with both COMPRESSORS running. I have checked the FSC and i would of thought that with the outside temperature at -0degrees today the FSC would not be working at full speed. Can anyone help........
Cheers
RBK36
-
01-12-2010, 10:51 PM #2
Re: Denco D28AVH
....and what is the evaporator doing?
Any temperatures to help us?Brian - Newton Abbot, Devon, UK
Retired March 2015
-
02-12-2010, 05:24 PM #3
Re: Denco D28AVH
When you say checked the fan speed controller have you tried adjusting it to raise the sys pressures slightly.
You have a huge pipe run there to influence the liquid line temps.
Particularly at this time of year.
Grizzly
-
03-12-2010, 06:27 PM #4
Re: Denco D28AVH
Hi Guys sorry been busy!!!!!
the evaporator was 11.2 degrees C, the suction pipe temp was about 7.8degrees C and the discharge pipe was 47degrees C. I switched the FSC off at the MCB and the head pressure went up and the unit tripped out. I have two other Denco units in the same data centre and the FSC were only doing 0.02Amps and 5.0Amps. If any of that helps let me know......
-
03-12-2010, 06:29 PM #5
Re: Denco D28AVH
sorry that was suppose to read 0.02amps and not 5.0Amps as the one i was working on.....
-
03-12-2010, 08:01 PM #6
Re: Denco D28AVH
A unit with 25kg of gas and the condenser fan is only taking 0.02 amps!?
Is the motor big enough?Brian - Newton Abbot, Devon, UK
Retired March 2015
-
09-12-2010, 02:37 PM #7
Re: Denco D28AVH
The max pipe run we allow is 100mts, at thats with a d28 (need to know the condenser) its 1 1/8 and 3/4 pipework.
At 100mts the refrigerant charge should be 36.2kgs per circuit.
I think you need to sort out you pipework first as its miles off.
Similar Threads
-
Manuals for Denco
By pavilion in forum Air ConditioningReplies: 12Last Post: 10-11-2010, 11:41 AM -
Denco Manuals
By pavilion in forum Air ConditioningReplies: 6Last Post: 29-09-2010, 10:13 PM -
Can't suss strange paramaters on Denco downflow unit
By Coolie in forum Air ConditioningReplies: 20Last Post: 26-07-2010, 03:20 PM -
Denco Close Control Units
By Freecool in forum Air ConditioningReplies: 12Last Post: 05-05-2010, 12:50 PM -
Denco Humidity Control
By chimayblnd in forum Air ConditioningReplies: 2Last Post: 08-04-2010, 12:48 PM