recovering 410a from scroll
Hey new to the field and not sure on the best way to recover 410a should the compressor be out of the loop and just pull it as a liquid from the line set or what?
Thanks
-
29-11-2010, 07:27 PM #2
Re: recovering 410a from scroll
The system should be shut down, and all valves opened attach your gauges to high and low side ports if available then recover in the normal way. the refrigerant should be recovered out of the compressor too.
-
30-11-2010, 01:55 PM #3
Re: recovering 410a from scroll
hey thanks!so there is no concern with pulling oil out of the compressor?
-
30-11-2010, 02:38 PM #4
-
30-11-2010, 03:45 PM #5
Re: recovering 410a from scroll
define normal ports
-
30-11-2010, 06:09 PM #6
Re: recovering 410a from scroll
suction, discharge and liquid line DO NOT try and recover from an oil drain port near the base of the compressor
-
10-12-2010, 11:19 PM #7
Re: recovering 410a from scroll
Hi I'm also new to recovering and am the proud owner of a new recovery unit.
It was supplied without a filter drier ? do I need one?
Can I use the recovery unit on 410a and r22 without cross contamination ?
Do i need 2 filter drier's (1 for each refrigerant)?
Any help and advice would be appreciated.
-
11-12-2010, 02:27 AM #8
Re: recovering 410a from scroll
Always remember to use a filter-dryer or particulate filter
on your refrigerant recovery unit. It is also important
to us an acid core dryer when recovering from a burned-out
system. Acid and particulate matter will cause damage
to your refrigerant recovery system. If you use the
appropriate filter on every job, your refrigerant recovery
equipment should give you many years of trouble-free service. Each filter should be labeled and used exclusively
for one type of refrigerant only.
-
11-12-2010, 03:24 AM #9
Re: recovering 410a from scroll
Here's a couple links that you should visit.
Pressurized while unbrazing
http://www.hvacrinfo.com/scroll_trouble.htm
4-1301
http://www.hvacrinfo.com/ae_index.htmThousands of HVACR manufacturers links! Visit: www.hvacrinfo.com
-
11-12-2010, 12:39 PM #10
Re: recovering 410a from scroll
One filter is good for all the refrigerants but vacuum also always your recovery unit. Otherwise moisture and air inside the unit will be pushed to your recovering bottle. So if you vacuum, you will pull out also the 'old' refrigerant.
But replace it at regular intervals.
I used/demonstrated in the last 2 years more than two thousand times a recovering cycle (with 3 different brands and 5 units total)
In Europe, you must recover till 0.3 bar absolute, so there will be always moisture and air ingress into the unit when leaving it some time in your van.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
Similar Threads
-
Digital Scroll VRF Systems & Inverter Systems
By weeliang82 in forum Air ConditioningReplies: 22Last Post: 16-11-2010, 04:07 PM -
Servicing a LG Mini Split 410a
By wrangoth in forum Trouble ShootingReplies: 8Last Post: 28-04-2010, 06:59 PM -
Scroll compressor for Freezing application
By georgedvf in forum Technical SpeculationsReplies: 18Last Post: 08-04-2010, 07:24 PM -
copeland scroll durability
By Third_techtrio in forum Technical DiscussionsReplies: 16Last Post: 23-01-2010, 04:47 AM -
Digital scroll
By archibaldtuttle in forum CommercialReplies: 3Last Post: 06-01-2010, 05:27 PM