    Hi Guys,
    When I do calculation of the heat loads on a refrigerated space I always count with a % for the ice formation on the coil, unless the temperature of the coil is high enough to ice formation.
    During ice formation the latent heat needed for the solidification of the water steal refrigeration capacity and so the air can't down so much is air temperature.
    Never had see this kind of heat load written on the engineering books but the true is that kind of heat load exist. Also never had see any one have this effect on account.
    Any comments?
    Aug 2007
    Sydney
    52
    1,083
    23
    Re: Heat load for cold store
    You need to research your subject further. You are incorrect - there is favorable ice formation to a certain extent, check massey university. It increases heat transfer. Then check coil bypass factor.
    Dec 2008
    Portugal
    48
    1,020
    Quote Originally Posted by Tesla View Post
    Sorry Tesla, BUT you are confusing/mixing the facts. I didn't mentioned about heat transfer efficiency, this is another subject. I'm talking about heat loads on a system/"box" where you must remove extra heat to frozen water.
    Aug 2009
    New Zealand
    2,554
    26
    You are talking about "air infiltration" and is a standard part of design in your heat load calculations.
    You need to know both wet and dry bulb conditions and how many air changes you expect
    3,362
    Sandro,
    All I know is most clients want cheapest job so air coolers are supplied for heat load etc etc .
    All looks good on paper but usually rooms don't perform or struggle due ,
    1/ Not allowing for a lot of defrosts if necassary so unit is not cooling in this period/s
    2/Not allowing for enough surface area on unit that has a % of ice on it in normal operation.
    Usually this means air coolers are 50% bigger than "normal".
    As you say for freezer or below 0 deg applications .
    Most don't perform when you want them to in summer etc.
    Dec 2008
    Portugal
    48
    1,020
    Quote Originally Posted by mad fridgie View Post
    Air infiltrations don't account the solidification of the water but only cooling and condensate. Besides that part of this water come from the product, then after it condensate it will be transform on ice (latent heat) so part of the cooling capacity will be used to the ice formation.
    Apr 2009
    South Africa
    49
    108
    Yes Sandro you are correct. When designing a cold/freezer room u have to know the entering temp of the product, the dew points of the product when placed in a freezer. The big thing is that u do not want to dry out the product and thus we normally bring down the superheat on the evaporators and up the surface area to get the same heat transfer(Kw r). Defrosting to many times also dry out the product especially if the product are not in plastic bag but open to the room atmosphere. Have u ever seen the moist that forms on the surface of any product after a long defrost period and the cooling cycle went back on? This moist forms because the skin of the product are giving of water as it is going through a dew point.
    Hope i explained it so that u understand that design differs from room to room depending on the product that are going to be stored.
    THE BEST WAY OF LEARNING IS TO DO IT YOURSELF!!!
    Apr 2009
    South Africa
    49
    108
  1. Calculating heat load
    By Abe in forum Technical Discussions
    Last Post: 13-08-2010, 05:40 PM
  2. Blast Freezer Heat Load calculations
    By smpsmp45 in forum NH3
    Last Post: 03-04-2010, 10:20 PM
  3. Heat load calculations Help!
    By jbomba in forum Technical Speculations
    Last Post: 17-10-2009, 11:12 AM
  4. Rule of thumb in heat load calculations
    By ronaldjaysonm in forum Tools and Calculators
    Last Post: 30-09-2009, 02:42 PM
  5. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Last Post: 28-05-2008, 01:08 AM