    subcooling



    Hi everyone,
    what is the advantage and disadvantge of subcooling? Thanks



  2. #2
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: subcooling

    advantages: more guarantees of no flash gas at the expansion valves (» better operation) due to friction on the pipes and hydrostatic penalization due to rising of the liquid. Also less mass flow of refrigerant (if the subcooling is significant » smaller pipes to and from the evaporator and also smaller volumetric displacement needed at the LP)
    To make progress is never good enough, I want to do better and better and better

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: subcooling

    Advantage: System works correctly
    Disadvantage: System does not correctly.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: subcooling

    Quote Originally Posted by Sandro Baptista View Post
    advantages: more guarantees of no flash gas at the expansion valves (» better operation) due to friction on the pipes and hydrostatic penalization due to rising of the liquid. Also less mass flow of refrigerant (if the subcooling is significant » smaller pipes to and from the evaporator and also smaller volumetric displacement needed at the LP)
    Some good points, Sandro.

    In my view, ensuring sufficient sub-cooling in order to minimise, or prevent flash-gas, is a real bonus. It allows the TXV, throttle device, to operate correctly, but, more importantly lowers the liquid line pressure drop.

    Lowering the liquid line pressure drop, in turn, reduces the high-side pressure required to push the liquid along the pipework. In other words, it can assist to reduce condenser pressure a few degrees. It should not be overlooked.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  5. #5
    Join Date
    Nov 2005
    Location
    belgium
    Posts
    61
    Rep Power
    0

    Re: subcooling

    hello evryone,
    with R404A, when i have a condening temp under the 40°C, then you see that the gas will stay in the condensor, if the recever has a glas, you can see the gas staying.
    so i think the best is to stay with a pressure high enough, pe 40°C, and after the condensor a evaporator to cool the liquid in temp.
    So we have a presure 19 bar (40°C) but a real temp of pe 25°C.
    i think correct?

  6. #6
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: subcooling

    The refrigerant in liquid state should be well drained from the condenser. So lower condensing pressure you can achieved » lower liquid saturated temperature and better volumetric efficiency of the compressor (» higher cooling capacity) also long life for the compressor...and better COP (the capacity will be higher and the power consumption will be lower).
    To make progress is never good enough, I want to do better and better and better

  7. #7
    Join Date
    Nov 2005
    Location
    belgium
    Posts
    61
    Rep Power
    0

    Re: subcooling

    yes i know this, but my problem is that when the condensor pressure is low, the gas will not flow to the evaporator.

  8. #8
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: subcooling

    But if it keeps retained on the condenser that means something wrong with condenser«»receiver. Double the DN of the discharge liquid pipe from the condenser to the receiver or mount another liquid line in parallel with the existing one.
    Also If the place where is the liquid receiver is warmer than the condensing temperature the problem can be reveled by what are you saying. Do you have an equalizing line between the inlet of the condenser and the liquid receiver?
    To make progress is never good enough, I want to do better and better and better

  9. #9
    Join Date
    Nov 2005
    Location
    belgium
    Posts
    61
    Rep Power
    0

    Re: subcooling

    no, this happens whole the time with standard units, pre fabricated. bitzer has on the receiver a eyeglass where you can see the level. the level stay high, but the eyeglass on the liquidline has flashgas, evaporator pressue lower.
    just make the pressure in the condensor higher and you see the gas flowing.

  10. #10
    Join Date
    Oct 2005
    Location
    Canada
    Posts
    35
    Rep Power
    0

    Re: subcooling

    LIQUID SUB-COOLING : is the reduction of refrigerant temperature in the liquid line below the saturation temperature
    BENEFIT
    - decrease electricity by lowering HP [by increasing refrigeration effect "RE"]
    - reduces maintenance/compressor run easier
    - reduces pull-down time after defrost

    example : compressor working at -45F suction, liquid supplied to the recirculator, will compare between +95F and +25F
    RE= 200/(595.6-70.2)= .38 LBS/MIN/TR [25F LIQUID] RE: 525 BTU/LB
    RF= 200(595.6-149.2)= .44 LBS/MINTR [95F LIQUID]
    RE: 446 BTU/LB

    17% IMPROVEMENT

    Regards
    Camille Zabbal

  11. #11
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: subcooling

    Camille,

    Pay attention to this example: condensing temperature +45șC with 5K subcooling is different of condensing temperature +40șC with 0K subcooling. In this last case the compressor will give more capacity, less power consumption and less maintenance.
    To make progress is never good enough, I want to do better and better and better

  12. #12
    Join Date
    Oct 2009
    Location
    USA
    Age
    67
    Posts
    28
    Rep Power
    0

    Re: subcooling

    Subcooling will increase the capacity in BTU's of the TXV. Which means you can design a smaller TXV for a evap coil. Example: No subcooling, you would have 5 ton TXV on a 5 ton coil. With subcooling you might use a 4.5 ton TXV on the same 5 ton coil. The 4.5 ton TXV will use a higher percent valve capacity and be more efficient. Sporlan has correction factors to calculate for subcooling. On a existing system, if you increase the subcooling temperature too low you will cause flood back to the compressor. Subcooling is highly recommend for freezers.

Similar Threads

  1. 9 superheat & subcooling scenarios
    By nike123 in forum Fundamentals
    Replies: 39
    Last Post: 19-07-2011, 03:16 AM
  2. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  3. Checking subcooling and superheat?
    By ZeroTolerance in forum Technical Discussions
    Replies: 6
    Last Post: 06-06-2010, 01:28 PM
  4. Subcooling
    By terryw in forum Supermarket Refrigeration
    Replies: 12
    Last Post: 07-03-2007, 09:53 AM
  5. Subcooling & Refrigerants
    By US Iceman in forum Fundamentals
    Replies: 40
    Last Post: 29-04-2006, 02:59 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •