    Capillary Sizing



    Could anyone please help regarding selecting a capillary tube for a single door commercial freezer using a Supco Bullet Restricto Capillary Kit?

    The compressor is a Cubigel GP14FB 3/8 HP on R134A but Supco's selection chart does not include this size compressor. The condenser is fan cooled but the evaporator is without a fan.

    I have attached Supco's sizing chart.

    Any other suggestions to what the capillary size should be or how to size the capillary would be greatly appreciated!
    Attached Images Attached Images



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Capillary Sizing

    Download Dancap from Danfoss and you can calculate just what you need.

    Remember that most cap tube sizing is an experiment.

    http://www.danfoss.com/BusinessAreas...ils/DanCap.htm

    Also, download the specification of that compressor if you don't already have it.
    http://www.hawco.co.uk/GP14FB-ECC-Cu...or_2246_p.aspx
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    vijitha1234's Avatar
    vijitha1234 Guest

    Re: Capillary Sizing

    let me know the test procedure to balance condenser water system for water cooled packages in a multy storied building please

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Capillary Sizing

    Quote Originally Posted by vijitha1234 View Post
    let me know the test procedure to balance condenser water system for water cooled packages in a multy storied building please
    What hast his to do wit capillary sizing?
    You must post this in the proper section
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Feb 2009
    Location
    England
    Posts
    8
    Rep Power
    0

    Re: Capillary Sizing

    Thanks for the advice Peter but I am not sure on finding some of the calculations needed with DanCap such as heat load of the system. I presume that the evaporating temp and the return gas temp will give the evaporator superheat differential??

  6. #6
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: Capillary Sizing

    hi
    referring to tecumseh its 2 meter 0.036 internal diameter

  7. #7
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    48
    Posts
    186
    Rep Power
    20

    Re: Capillary Sizing

    I have always trusted to use the DANCAP program which Brian has prescribed above.

  8. #8
    Join Date
    Oct 2008
    Location
    New Zealand
    Age
    46
    Posts
    33
    Rep Power
    0

    Re: Capillary Sizing

    1.9m 0.042 for single feed evap on this comp

  9. #9
    Join Date
    Jul 2007
    Location
    Sweden
    Age
    50
    Posts
    9
    Rep Power
    0

    Re: Capillary Sizing

    DanCap seems to be a good software, but could someone please let me know, how to estimate the heatload in a easy way for any specifik unit ? For example, it can be tricky to estimate the heat load for a bottle fridge when one wants to change the cap.tube. Kind regards / Tobias

  10. #10
    Join Date
    Dec 2008
    Location
    USA
    Age
    41
    Posts
    58
    Rep Power
    16

    Re: Capillary Sizing

    Software or no software. The cap tube primary purpose is to meter the amount of refrigerant getting to a specific part of the refrigerant circuit. So what you need to know is how much flow through the original cap tube and match up a size and length that will do the same.

Similar Threads

  1. Capillary tube sizing
    By Sledge in forum Refrigerants
    Replies: 7
    Last Post: 17-11-2010, 12:44 AM
  2. capillary tube sizing
    By juliushhill in forum Fundamentals
    Replies: 8
    Last Post: 16-03-2010, 04:24 PM
  3. capillary sizing for R404a
    By ding in forum Technical Speculations
    Replies: 8
    Last Post: 19-03-2008, 08:27 PM
  4. Capillary tube sizing
    By SULTAN in forum Trouble Shooting
    Replies: 3
    Last Post: 28-12-2007, 06:27 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •