Results 1 to 10 of 10
    Feb 2009
    8
    Capillary Sizing
    Could anyone please help regarding selecting a capillary tube for a single door commercial freezer using a Supco Bullet Restricto Capillary Kit?
    The compressor is a Cubigel GP14FB 3/8 HP on R134A but Supco's selection chart does not include this size compressor. The condenser is fan cooled but the evaporator is without a fan.
    I have attached Supco's sizing chart.
    Any other suggestions to what the capillary size should be or how to size the capillary would be greatly appreciated!
    10,503
    Re: Capillary Sizing
    Download Dancap from Danfoss and you can calculate just what you need.
    Remember that most cap tube sizing is an experiment.
    http://www.danfoss.com/BusinessAreas...ils/DanCap.htm
    Also, download the specification of that compressor if you don't already have it.
    http://www.hawco.co.uk/GP14FB-ECC-Cu...or_2246_p.aspx
    vijitha1234's Avatar
    vijitha1234 Guest
    let me know the test procedure to balance condenser water system for water cooled packages in a multy storied building please
    Oct 2003
    56
    5,519
    28
    Quote Originally Posted by vijitha1234 View Post
    What hast his to do wit capillary sizing?
    You must post this in the proper section
    Feb 2009
    8
    Thanks for the advice Peter but I am not sure on finding some of the calculations needed with DanCap such as heat load of the system. I presume that the evaporating temp and the return gas temp will give the evaporator superheat differential??
    lebanon
    130
    11
    hi
    referring to tecumseh its 2 meter 0.036 internal diameter
    Republic of south africa
    42
    186
    14
    I have always trusted to use the DANCAP program which Brian has prescribed above.
    Oct 2008
    New Zealand
    40
    1.9m 0.042 for single feed evap on this comp
    Jul 2007
    Sweden
    43
    9
    DanCap seems to be a good software, but could someone please let me know, how to estimate the heatload in a easy way for any specifik unit ? For example, it can be tricky to estimate the heat load for a bottle fridge when one wants to change the cap.tube. Kind regards / Tobias
    Dec 2008
    35
    58
    10
    Software or no software. The cap tube primary purpose is to meter the amount of refrigerant getting to a specific part of the refrigerant circuit. So what you need to know is how much flow through the original cap tube and match up a size and length that will do the same.
  1. Capillary tube sizing
    By Sledge in forum Refrigerants
    Last Post: 17-11-2010, 12:44 AM
  2. capillary tube sizing
    By juliushhill in forum Fundamentals
    Last Post: 16-03-2010, 04:24 PM
  3. capillary sizing for R404a
    By ding in forum Technical Speculations
    Last Post: 19-03-2008, 08:27 PM
  4. Capillary tube sizing
    By SULTAN in forum Trouble Shooting
    Last Post: 28-12-2007, 06:27 PM