    What psi should you pressure test a split at



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Psi

    james , tell me what are you pressure testing with? and what gas are you going to use in the unit?

  3. #3
    Jameswilkinson's Avatar
    Jameswilkinson Guest

    Re: Psi

    R134a on a college work shop fridge system sorry not split

  4. #4
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Psi

    Quote Originally Posted by Jameswilkinson View Post
    R134a on a college work shop fridge system sorry not split
    Map x 1.3 for pressure test
    map x 1.1 for leak test
    MAP= REFRIGERANT PRESSURE AT 55C AIR COOLED)(45C WATER COOLED
    MAP- maximum allowable pressure
    But your tutor should have told you this before setting you the problem also you should be working in Bar unless your in Dartford USA
    Last edited by james10; 22-11-2010 at 05:53 PM.

  5. #5
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Psi

    Quote Originally Posted by james10 View Post
    But your tutor should have told you this before setting you the problem also you should be working in Bar unless your in Dartford USA

    Bar, psi, can't see why the units of measurment make a difference. If you want to go really Euro then wouldn't Pascals be better as that it is the SI unit?

    Use the factors as mentioned above for official strength and leak testing. You will need to use gauge pressure as opposed to absolute.

    Cheers,

    Andy.
    Health and safety first..........unless I'm in a hurry.

  6. #6
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Psi

    Quote Originally Posted by Tayters View Post
    Bar, psi, can't see why the units of measurment make a difference. If you want to go really Euro then wouldn't Pascals be better as that it is the SI unit?

    Use the factors as mentioned above for official strength and leak testing. You will need to use gauge pressure as opposed to absolute.

    Cheers,

    Andy.
    When i did my nvq all the exam questions were in Barg for someone starting out i thought it would make life easier to keep it simple nothing, to do with the europrats, myself i work in kpa i think it comes down to preference.

  7. #7
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Psi

    Hi James,

    Sorry, I see where your post was coming from now.

    I assumed the Euro link as that was the only reason I could see why it would be measured in Bar. Still, as the old man always told me - never assume.

    Quote Originally Posted by james10 View Post
    But your tutor should have told you this before setting you the problem also you should be working in Bar unless your in Dartford USA
    I remember in the first year of college the tutor telling us 'you can't teach someone how to braze, you can either do it or you can't'. Sounds like the same bloke!

    Cheers,

    Andy.
    Health and safety first..........unless I'm in a hurry.