    Coldstore Lighting



    Guys,

    I'm looking for lighting that is good for -25 deg C and 0 deg C application. Who are the better brands to recommend.
    THX...



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Coldstore Lighting

    Hi Kevin,

    24V bulbs are widely used, I know that Danfoss, makes speciat sterters for neon that will start at low temp.

    I use 240V bulbs, in a housing IP65.

    Chemi

  3. #3
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    61
    Posts
    589
    Rep Power
    19

    Re: Coldstore Lighting

    Go to your local electrical wholesaler dont buy arctic rated lights at £££££'s instead buy the plastic twin tube fittings with the diffuser/cover that clips into place, these ARE rated for -25oC and a fraction of the price.

  4. #4
    Join Date
    Jan 2006
    Location
    canada
    Posts
    5
    Rep Power
    0

    Re: Coldstore Lighting

    Any metal halide fixture with a low temperature ballast is good for cold storage rooms. The only challange is that they are slow starting even in heated warehouses. However, they run very economically.

  5. #5
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    517
    Rep Power
    19

    Re: Coldstore Lighting

    Weve been using metal haide in freezers for years and they work great, we recently added motion sensors to the lighting and seems to workking so far, so when no one is in the room the lights go out
    Last edited by nh3wizard; 29-08-2006 at 06:34 PM. Reason: Add information

  6. #6
    Join Date
    Oct 2002
    Location
    scotland
    Age
    56
    Posts
    16
    Rep Power
    0

    Re: Coldstore Lighting

    had lots of problems with tubes and control gear failing best to leave light on when in a low temp enviroment
    saves on cost of replacing tube/ballasts/starters and also cost of labour which is constantly rising thus offsetting cost of energy

  7. #7
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: Coldstore Lighting

    Hi

    Seen Mercury vapour and Sodium fittings used in freezers, slow to start, but economic to run

    Kind Regards. Andy

  8. #8
    luvai's Avatar
    luvai Guest

    Re: Coldstore Lighting

    Quote Originally Posted by Andy View Post
    Hi

    Seen Mercury vapour and Sodium fittings used in freezers, slow to start, but economic to run

    Kind Regards. Andy
    Andy,
    Hi ! I need to work on a cold storage for an ice cream factory whose requirement is -40 C. Can you recommend a source for procuring such lights and also throw some LIGHT on thetype of lights recomended.

    Regards
    Luvai

  9. #9
    Join Date
    May 2007
    Location
    India
    Posts
    695
    Rep Power
    17

    Re: Coldstore Lighting

    We use Either Philips or Zumtobel or Glamox fittings for temp upto -40 deg c.

    Absolutely no problems. We have used over 4500 fittings uptill now

  10. #10
    Peter Russell's Avatar
    Peter Russell Guest

    Re: Coldstore Lighting

    Hi , We have developed an IP65 L.E.D light fitting which is perfect for cold store and freezer lighting . No Maintenance for 50,000 hours and also each individual light fitting is fitted with a PIR control which allows the fitting to be switched off or dimmed to 10 percent at non occupancy . These fittings run at 35 watts fully on or 3 watts in the dimming mode. Also available as an emergency light with 3 hour battery back up .

    Cheers Pete

  11. #11
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    517
    Rep Power
    19

    Re: Coldstore Lighting

    Flourescent lighting has come along way... You might want to look in this direction

  12. #12
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Coldstore Lighting

    came across one install were they cut a square hole in roof panel,sealed it both sides with clear acrylic and sat the cheap mercury halide on top,easy to service and install
    mmm to beer or not to beer...........lets drink breakfast

  13. #13
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: Coldstore Lighting

    kevin Yeo
    It is very import in lighting to consider the type of coldstore you are working on.
    The light affect the color or aparence of the storaged goods.
    Also if the worker need read or observe the steekers on the pallets

    MH or flourecent are white color
    Sodio and incandecent are warm colors

    Regards
    Gwapa

  14. #14
    Michael Raeuber's Avatar
    Michael Raeuber Guest

    Re: Coldstore Lighting

    Hi Peter

    we are constructing a new coldstorage and are interested in your light fitting. Our rooms are - 25 C, 10 rooms. Need lighting for alleys, blastfreezer rooms and processing/chiller rooms as well.
    Could you give me the technical specs of your lights and a price offer to
    michael.raeuber@royalcargo.com
    We are in the Philippines, but have a subsidiary company in the UK which is in the transport business

    best regards

    Michael K Raeuber


    Quote Originally Posted by Peter Russell View Post
    Hi , We have developed an IP65 L.E.D light fitting which is perfect for cold store and freezer lighting . No Maintenance for 50,000 hours and also each individual light fitting is fitted with a PIR control which allows the fitting to be switched off or dimmed to 10 percent at non occupancy . These fittings run at 35 watts fully on or 3 watts in the dimming mode. Also available as an emergency light with 3 hour battery back up .

    Cheers Pete

  15. #15
    Join Date
    Oct 2007
    Location
    ENGLAND
    Posts
    27
    Rep Power
    0

    Re: Coldstore Lighting

    er 1 2 much im off 2 bed sorry (oow he gose like the clappers dunt he)

  16. #16
    phil dillon's Avatar
    phil dillon Guest

    Re: Coldstore Lighting

    Quote Originally Posted by Peter Russell View Post
    Hi , We have developed an IP65 L.E.D light fitting which is perfect for cold store and freezer lighting . No Maintenance for 50,000 hours and also each individual light fitting is fitted with a PIR control which allows the fitting to be switched off or dimmed to 10 percent at non occupancy . These fittings run at 35 watts fully on or 3 watts in the dimming mode. Also available as an emergency light with 3 hour battery back up .

    Cheers Pete
    Hi Pete interested have you got a website

  17. #17
    Julian Riddle's Avatar
    Julian Riddle Guest

    Re: Coldstore Lighting

    LED is the way to go but retrofit cost is an issue.
    Technology is still verry new,efficiency and cost will improve.In 2 years it will be a verry efficient prospect and a great green light for all.

  18. #18
    Robert Zewald's Avatar
    Robert Zewald Guest

    Exclamation Re: Coldstore Lighting

    NEDAP LUXON: INNOVATIVE e-HID LIGHTING FOR CONDITIONED AND COLD STORAGE WAREHOUSING

    HID lighting is ideal for low temperature applications and its lumen output is not affected by the extreme temperatures as low as -28 degrees Celsius. The innovative Nedap Luxon electronic HID ballast offers a significant opportunity to introduce sustainable lighting for Cold Storage and Conditioned Warehousing. The Nedap Luxon e-HID ballast is 10% more energy efficient than outdated magnetic HID ballast units. Secondly, it is now possible to continuously dim and let the HID lamps operate between 50 and 100% of the standard lamp power. Less heath will be generated, which results in a double kick back for energy cost reductions.

    Because the e-HID ballast will cause less blackening of the lamp arc tube, it results in a higher lumen/W yield throughout the lamp life. With more lumen output it is possible for retrofit projects to replace a typical 400W magnetic HID installation with a 250 or 320W Nedap Luxon luminaire. Another important feature of the new e-HID electronics is the extended lamp life up to a double life time. This reduces the maintenance costs and lamp waste.

    Optional for the Nedap Luxon e-HID ballast is the build-in antenna function. It enables the system to operate as a wireless platform with every ballast unit connected to the Luxon Central Processing Unit. Lamps can be controlled one by one or can function in groups. With the wireless connectivity the lamp settings are easily managed from a computer and can follow any future floor reorganisation. Most importantly, all lamp data are gathered and processed. This creates a powerful Lighting Management software tool: lamp status, lamp failure report by e-mail, lamp operating hours, real time energy consumption and savings, carbon savings and more. From any location one or multiple lighting networks can be monitored. Preventive maintenance and re-lamping is possible when the lamp burning hours enter or exceed the maximum lamp operating hours defined.

    The Luxon Central Processing Unit can be connected to a building management system and let the HID lighting groups be integrated with the order picking program. It means that lamps will be ignited only for those aisles where goods will be picked and handled. The Nedap Luxon e-HID solution is ideal for new high-bay installations and for lighting retrofits. Several Cold Storage installations in Europe already operate on this principle and have achieved significant energy savings of 30-65%. With a payback time of 1-2 years it almost becomes a no-brainer. Visit nedap-luxon.com

  19. #19
    Join Date
    May 2007
    Location
    India
    Posts
    695
    Rep Power
    17

    Re: Coldstore Lighting

    Interesting write up

  20. #20
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Coldstore Lighting

    Quote Originally Posted by Robert Zewald View Post
    NEDAP LUXON: INNOVATIVE e-HID LIGHTING FOR CONDITIONED AND COLD STORAGE WAREHOUSING

    HID lighting is ideal for low temperature applications and its lumen output is not affected by the extreme temperatures as low as -28 degrees Celsius. The innovative Nedap Luxon electronic HID ballast offers a significant opportunity to introduce sustainable lighting for Cold Storage and Conditioned Warehousing. The Nedap Luxon e-HID ballast is 10% more energy efficient than outdated magnetic HID ballast units. Secondly, it is now possible to continuously dim and let the HID lamps operate between 50 and 100% of the standard lamp power. Less heath will be generated, which results in a double kick back for energy cost reductions.

    Because the e-HID ballast will cause less blackening of the lamp arc tube, it results in a higher lumen/W yield throughout the lamp life. With more lumen output it is possible for retrofit projects to replace a typical 400W magnetic HID installation with a 250 or 320W Nedap Luxon luminaire. Another important feature of the new e-HID electronics is the extended lamp life up to a double life time. This reduces the maintenance costs and lamp waste.

    Optional for the Nedap Luxon e-HID ballast is the build-in antenna function. It enables the system to operate as a wireless platform with every ballast unit connected to the Luxon Central Processing Unit. Lamps can be controlled one by one or can function in groups. With the wireless connectivity the lamp settings are easily managed from a computer and can follow any future floor reorganisation. Most importantly, all lamp data are gathered and processed. This creates a powerful Lighting Management software tool: lamp status, lamp failure report by e-mail, lamp operating hours, real time energy consumption and savings, carbon savings and more. From any location one or multiple lighting networks can be monitored. Preventive maintenance and re-lamping is possible when the lamp burning hours enter or exceed the maximum lamp operating hours defined.

    The Luxon Central Processing Unit can be connected to a building management system and let the HID lighting groups be integrated with the order picking program. It means that lamps will be ignited only for those aisles where goods will be picked and handled. The Nedap Luxon e-HID solution is ideal for new high-bay installations and for lighting retrofits. Several Cold Storage installations in Europe already operate on this principle and have achieved significant energy savings of 30-65%. With a payback time of 1-2 years it almost becomes a no-brainer. Visit nedap-luxon.com
    It would be good to see the numbers about energy savings and payback. How did you get 30-65% and 1-2 years?

  21. #21
    Robert Zewald's Avatar
    Robert Zewald Guest

    Re: Coldstore Lighting

    Hi Segei,
    *10% higher ballast efficiency
    *20% lumen maintenance (400-> 320W)
    *additional savings through Dimming
    *additional savings through savings on cooling with less heath from HID lunits
    *additional savings due to less maintenance on relampingg