    Temp alarm required



    Hello everyone,

    We have been asked to look after a small walk in freezer (not installed by ourselfs) which has been causing a few problems recently. The first time it went off (gas leak) we were able to save the food, next time (another leak) was not so lucky as it was the weekend and no one was in that part of the building, everything had to be binned.

    We have been asked to sort out the pipe work as the pipes have rubbed through both times and install a temperature alarm to the room which will alarm into a corridor and alert the security guard who can then inform the relevant person.

    Can anyone suggest a sensibly priced alarm system which would be suitable?

    Thanks in advance.



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Temp alarm required

    you can get an carel for around £100 with ntc probe temp input with a high temp output try rs you might find thier own brand equvilent cheaper

  3. #3
    Join Date
    Feb 2007
    Location
    newcastle but now carlisle
    Age
    53
    Posts
    195
    Rep Power
    18

    Re: Temp alarm required

    fit a stat on the coldroom and a light/buzzer in the corridor . it will not cost that much !! keep it simple

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Temp alarm required

    Use an Eliwell/Dixell/Carel or similar to monitor the temperature.

    Connect it to a simple lamp or if you want audible as well get an alarm beacon from someone like RS.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: Temp alarm required

    as tony says fit a simple ranco or danfoss stat to it add a flashing light or buzzer, costs about £30 all in and 45 mins to install, this i s much cheaper than the electronic route

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Temp alarm required

    Select an electronic controller with an alarm out put clean contact that can be connected to the security alarm, identify it as a temp alarm, and allow a 1 hour delay before alarming. Covers the problem when client is off site, and a whole lot cheaper that the greif of an insurance claim.

Similar Threads

  1. Carrier Transicold Container Problem
    By Shamel in forum Transport
    Replies: 39
    Last Post: 23-01-2012, 11:23 PM
  2. Lower Air off temp required
    By Collie in forum Air Conditioning
    Replies: 12
    Last Post: 22-07-2010, 05:53 PM
  3. Replies: 5
    Last Post: 08-11-2009, 05:10 PM
  4. Replies: 3
    Last Post: 13-06-2009, 01:39 PM
  5. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •