    Pressure variation



    Hi I have been working on the walk in fridge on Tuesday and after checking pressure on shrader valve gauge started to rising from 1.5 to 3 bars then stayed there for a minute just to drop to 1 bar and rised again up yo 2 bars then up to 3 basically the pressure gauge was playing around and didn't sabilize at all.what can be wrong in situation like this???
    P;ease help Iam new to this job.



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Pressure variation

    Hi propper ,
    are you saying whilst you had your vac pump on the psi raised?

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pressure variation

    Is this one compressor and one evaporator system or you have multiple evaporators on one compressor?

  4. #4
    Join Date
    Oct 2010
    Location
    UK
    Age
    39
    Posts
    33
    Rep Power
    0

    Re: Pressure variation

    Hi there was one evaporator and one compresor wich was outside basically it was annual service so i just connected gauge blue to check pressure and then this start happening after words.I started job this week person Iam learning off isn't much expirience too so we just connect gauge to shreder valve and that what start happening there was no vac as far as iam concerned at all.Iam confused cause I have no one who could explain anything to me realy .How do you check presssure on service properly. Plus fridge was not going down at all stayed about 5 6 degrees while set to 2 altough kitchen stuff all the time kept opening doors and also evaporator was a bit iced up so we deiced it with powertorch .Please help.

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Pressure variation

    It sounds as if you are short cycling on LP.
    You need to establish your operating pressures and temperatures.
    Basically a blocked evaporator will drop the system LP like a stone.
    Also the excessive ice build up on the evap will compound the situation.
    Deice the evap,set the system to work and monitor your operating pressures and temps.
    Your kitchen staff movements may well be an issue?
    As each time they enter they will be adding moisture.
    Are there curtain strips across the threshold?
    Let us know how you get on.
    Grizzly

  6. #6
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Pressure variation

    properdouble, all you are telling us is that you are not safe to work on your own , you connected the blue gauge that's the suction side, but where did you connect it too?
    you say it was 56 degrees?
    the unit has to run with your gauges on , in the right shrader points, blue to the suction red to the discharge and with all the valves closed on your gauges then with your compariter, with experiance you will be able to see what the fridge is doing

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Pressure variation

    Pressure doesn't tell us anything if we don't know what refrigerant is in the system.

  8. #8
    Join Date
    Jan 2009
    Location
    Australia
    Age
    60
    Posts
    108
    Rep Power
    16

    Re: Pressure variation

    There's some good reading around this forum - particularly in the Fundementals section which I think will be of benefit. You probably need to be doing a lot of reading and understanding or you may end up turning your plant (or someone else's) into a boat anchor. It's easy to do if you don't have enough knowledge.

  9. #9
    Join Date
    Oct 2010
    Location
    UK
    Age
    39
    Posts
    33
    Rep Power
    0

    Re: Pressure variation

    I meant 5 maybe 6 degrees not 56 .I have connected gauge blue to the law pressure shrader valve near compressor on the condensing unit.Fridge was working apart from iced up evaporator and pressure variation during the test.I just wanted ask what could be wrong what sort of remedial put in this case after service should it be :full leak check,faulty defrost probe as far as i remember there was no curtains.

Similar Threads

  1. NVQ 3 online test
    By Burrah Boy in forum Training
    Replies: 7
    Last Post: 28-10-2009, 08:35 PM
  2. Effect of inverter on Pressure Ratio
    By GIB in forum Air Conditioning
    Replies: 6
    Last Post: 03-10-2009, 01:54 PM
  3. How can I reduce evaporator pressure?
    By mansari in forum Fundamentals
    Replies: 29
    Last Post: 05-09-2009, 01:59 AM
  4. Replies: 27
    Last Post: 27-10-2006, 03:19 AM
  5. TEV capacity related to pressure drop
    By DaBit in forum CPU Overclockers
    Replies: 8
    Last Post: 06-12-2002, 05:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •