Thread: danfoss ekc 531b
-
18-11-2010, 10:41 PM #1
danfoss ekc 531b
Got a dual temp rack with 10 comps run by the above controller, my problem is that comps 2,4,6,8,10 are showing alarm and will not run, anyone had this sort of problem.
This is not effecting cabinet temps on short floor, and i am stumpped
-
18-11-2010, 11:27 PM #2
Re: danfoss ekc 531b
Have you checked the alarm circuit connections to see if there is an alarm state active?
http://www.google.co.uk/url?sa=t&sou...q-3r8g&cad=rjaBrian - Newton Abbot, Devon, UK
Retired March 2015
-
19-11-2010, 02:03 PM #3
Re: danfoss ekc 531b
Could be a whole host of problems without a handset, or a front end and without the paperwork your pissing in the wind, i have a spare booard if you need 1 though
-
21-11-2010, 04:57 PM #4
Re: danfoss ekc 531b
If the inputs on that compressors are open, the outputs are also open and the compressors will not run. Did you check the inputs (safety circuit like overloads, hp/lp controls etc.)
Is there an EKA 162 Push Button Display connected to the 531?I am not always right, but I'm never wrong!