    High cop



    This is beyond my brain today!
    If you have a room heating load of say 8kW and install a 12kW inverter heat pump system will the COP be higher than a 8kW system installed for the same heating load.
    The thinking is this, the evaporator and condenser coils are oversized and the compressor will never need to run at full speed so power consumption will be less for the given capacity than the correctly sized system.
    Am I missing something here?
    Thanks



  2. #2
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: High cop

    The larger heat exchangers and slow speed of the compressor will make for a more efficient heat pump until the controls or the limitations of the compressor get in the way of you taking advantage of those bigger heat exchangers....And at nominal 66% loading it won't be an issue. But if your control arrangement lets this system drop to (say) 20% speed when the actual requirement is only 30% of the nominal: almost any type of compressor and at least a few inverters are going to give you issues.

  3. #3
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: High cop

    Twas on the day of salstice winter, that solitude in the retarded form, beggatted a poster of motor terminals name. One more time a key did he use, to twist the mood of forum folk, "like the power of time on the mantle peice, replenishment not at this moment needed." But still persistent in his quest, which may include potential discipline maybe yet, or even attention from moderator senses, along with vendetta of forum folk.

  4. #4
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: High cop

    ah, you speaketh the truth, chilly

Similar Threads

  1. Over charged system... what symptoms?
    By Clk320_Greg in forum Trouble Shooting
    Replies: 2
    Last Post: 19-10-2009, 06:25 PM
  2. What is a High suction pressure ?
    By kfjoe in forum Fundamentals
    Replies: 7
    Last Post: 14-09-2009, 07:16 AM
  3. need help! compressor kicking out on high pressure
    By SloFuse in forum Trouble Shooting
    Replies: 16
    Last Post: 19-08-2009, 04:46 PM
  4. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  5. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •