Appropriate thickness of rubber insulation
Need help re: appropriate thickness of rubber insulation needed for a low temp. refrigeration system with an evaporating temp of -38 degC. We need to replaced the old one since it is already developed a condensation that is really keeping the ceiling of the room where the pipe runs wet all the times especially when it defrost (hot gas defrost).
Thanks,
-
17-11-2010, 02:56 AM #2
-
23-12-2010, 06:55 PM #3
Re: Appropriate thickness of rubber insulation
-
24-12-2010, 04:59 AM #4
Re: Appropriate thickness of rubber insulation
You will need at least 60mm to avoid condensation there,,,,,i would not think about using rubber as it will eventually fail,,,look at using polyeurethane at least 50mm thick would be a starting point if yoou want it done right.Lawrie
-
24-12-2010, 05:05 AM #5
Re: Appropriate thickness of rubber insulation
For low temperatures Polyurethane foam is better suited than Nitrile rubber.
-
24-12-2010, 12:05 PM #6
Re: Appropriate thickness of rubber insulation
Thanks guys, it will help a lot.