    Bojan Bojanic's Avatar
    Bojan Bojanic Guest
    SuperHeat Setting
    Hi All,
    Got a bit of a debate going here about setting superheats.
    Case:
    Evaporator temperature (converted from pressure)
    -24 Celsius
    Temperature at the bulb -20
    Is that a correct way to set 4K superheat or should the temperature at the bulb be -28??
    38
    Re: SuperHeat Setting
    Hi Bojan.
    go to www.kueba.de and look for the service tools area.
    3,853
    Found this on the sporlan/parker site
    http://www.parker.com/literature/Spo...nous/Form1.pdf
    Basically if you are evaporating at -4C for example which you have determined by taking the pressure at the evaporator outlet and converting that pressure into temperature with a pt chart, you then take the temperature at the outlet and compare the two, say its 3C then you have 7K superheat. Its K for Kelvin as its a difference in temperature and not an actual temperature.
    Jon
    Last edited by monkey spanners; 23-12-2010 at 11:04 PM. Reason: must type quicker!!!!!!
    Oct 2003
    5,630
    Quote Originally Posted by Bojan Bojanic View Post
    -24 Celsius
    You have indeed 4K superheat, if you should have -28°C, then you have subcooled instead of superheated gas.
    Which isn't possible in an evaporator.