Design condensing temperature for Dammam, Saudi Arabia
Good day,
What would be the optimal, design, condensing temperature for an R717 plant in Dammam, Saudi Arabia?
Regards,
-
10-11-2010, 02:52 PM #2
Re: Design condensing temperature for Dammam, Saudi Arabia
60°C for air cooled condenser
-
11-11-2010, 11:42 PM #3
-
12-11-2010, 12:15 PM #4
Re: Design condensing temperature for Dammam, Saudi Arabia
I worked in Dammam for years. All of the plants I worked on were ammonia systems with evap. condensers. We had no problem designing for 40 degrees condensing & no problem maintaining 35 to 38 degrees saturated condensing temperature in practice. Summer temperatures can reach 50 for almost a month so air cooled condensing should be designed for at least 60.
-
16-11-2010, 08:37 AM #5
Re: Design condensing temperature for Dammam, Saudi Arabia
Thank you Charlie