    Compressor power?



    Hi, I need to cool 200 liter of water from 22°C down to 2°C in 2 hour time. How to determine how much BTU do I need in order to do that?

    Thanks in advance.



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Compressor power?

    mcΔt

    m=mass 200ltr
    c =1 for water
    Δt=22-2=20
    total capacity per hour = 200x1x20=4000kcal\2=2000kcal
    And thats equals about 8000btuh
    Last edited by chemi-cool; 07-03-2011 at 04:51 PM.

  3. #3
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Compressor power?

    Q=mc(t2-t1) or Q= m*c* Δt
    Q=200*1(22-2)
    Q=200*20
    Q=4000 Kcal
    Q= 2000 Kcal/h

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Compressor power?

    Q = L/sec x specific heat x delta T 'K
    Q = 200/7200sec x 4.186 Kj/Kg' K x 20'K
    Q = 2.3256 Kw x 3517
    Q = 8178.97 Btus / hour