Results 1 to 16 of 16
  1. #1
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    7 Subcool & Superheat Problem Scenarios



    I'm not going to help anyone with any clues.

    There are a few of our employees and subbies out there who know the answers - please don't pass clues.

    What is the problem with the system in each of the subcool and superheat combination scenarios?

    The scenarios are based on Gary Lloyd's eliminative principles.
    Attached Images Attached Images



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: 7 Subcool & Superheat Problem Scenarios

    Probably too simplistic... but interesting for developing diagnosing skill

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: 7 Subcool & Superheat Problem Scenarios

    First, is this capilary or TXV or electronic expansion valve controled sistem?

  4. #4
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: 7 Subcool & Superheat Problem Scenarios

    Secondly does it have Head Pressure Control?
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  5. #5
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: 7 Subcool & Superheat Problem Scenarios

    You're asking for too many clues

  6. #6
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: 7 Subcool & Superheat Problem Scenarios

    NNN - this is probably too advanced for you.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: 7 Subcool & Superheat Problem Scenarios

    Quote Originally Posted by DTLarca View Post
    You're asking for too many clues
    Same scenario with different expansion device gives different answer. Without knowing that, I suppose, it cannot be correctly answered.

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: 7 Subcool & Superheat Problem Scenarios

    Quote Originally Posted by DTLarca View Post
    NNN - this is probably too advanced for you.
    Aahahaha... as far as I'm concerned the 7 scenarios do not show any problem. All of the combinations are perfectly suitable for any system, considering that "norm" SC and SH are generally not published, and a difference of few K may well be the tolerance of the field instrumentation of different engineers.
    But if you are reaching the orgasm with this simplistic tests, go ahead, and make your day.

  9. #9
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: 7 Subcool & Superheat Problem Scenarios

    In other words too complicated for you

  10. #10
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: 7 Subcool & Superheat Problem Scenarios

    Okay Nike - good question - so, just one clue: only TEV and Cap-Tube relevant here.

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: 7 Subcool & Superheat Problem Scenarios

    Quote Originally Posted by DTLarca View Post
    Okay Nike - good question - so, just one clue: only TEV and Cap-Tube relevant here.
    That is not clue at all.
    TXV and capillary tube system with different superheat and subcooling values could be perfectly OK.
    Make up your mind and tell us what is expansion device used in this scenarios.

    I like these scenarios. Pretty much less misleading.
    Last edited by nike123; 08-11-2010 at 02:58 PM.

  12. #12
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: 7 Subcool & Superheat Problem Scenarios

    Both TEV and cap-tube expansion devices are relevent to the scenarios - a skilled subcool and superheat troubleshooter will look at the numbers given and know which readings are from a cap-tube circuit and which are from TEV circuit.

  13. #13
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: 7 Subcool & Superheat Problem Scenarios

    Quote Originally Posted by DTLarca View Post
    In other words too complicated for you
    In other words, let me translate it for you, the 7 scenarios do not show any problem in themselves.
    Publishing a list of SH and SC out of context just constitutes poor teaching practice.

    For your knowledge, I am a member of Ashrae technical commitee TC9.9 and writer for the most popular HVAC teaching and formation magazine in my country.

    Please don't take your time explaining who you are, because I don't give a f--k. You are the first proud member of my ignore list, and that's enough for me.

  14. #14
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: 7 Subcool & Superheat Problem Scenarios

    Quote Originally Posted by NoNickName View Post
    In other words, let me translate it for you, the 7 scenarios do not show any problem in themselves.
    Publishing a list of SH and SC out of context just constitutes poor teaching practice.
    There is a very clearly defined context. It need be no more distinct.

    1. The scenarios are based on Gary Lloyds Illiminative Principles.
    2. The first row of numbers indicate the same system when all is good.
    3. Sometimes the system has a cap-tube and sometimes a TEV.
    Quote Originally Posted by NoNickName View Post
    For your knowledge, I am a member of Ashrae technical commitee TC9.9 and writer for the most popular HVAC teaching and formation magazine in my country.
    I don't doubt that - I think you do have some good knowledge from what I've read. But you are also quite naive. I'd be happy to show you all the technical errors or vagaries in your articles

  15. #15
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: 7 Subcool & Superheat Problem Scenarios

    There`s only one way to settle this.
    In the words of Harry Hill "FIGHT!!!!!!!"

  16. #16
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: 7 Subcool & Superheat Problem Scenarios

    Quote Originally Posted by DTLarca View Post
    Both TEV and cap-tube expansion devices are relevent to the scenarios - a skilled subcool and superheat troubleshooter will look at the numbers given and know which readings are from a cap-tube circuit and which are from TEV circuit.
    Well, lets see. For #3, 2k sub and 10k super...capillary system working hard, high condenser and evap loads.... OR, tev system with high evap load. Either way,not enough info for correct assessment. To be bold, 2k sub could represent undercharged and shot condenser with 2 of 3 fans dead on a cool day. Mike.

Similar Threads

  1. understanding superheat.
    By The_Apprentice in forum Technical Discussions
    Replies: 8
    Last Post: 08-10-2010, 01:01 PM
  2. superheat ahd subcooling
    By jonc5553 in forum Fundamentals
    Replies: 3
    Last Post: 06-08-2010, 12:37 AM
  3. Saunier Duval Problem
    By mallorcanangel in forum Air Conditioning
    Replies: 1
    Last Post: 10-07-2009, 01:26 AM
  4. Low superheat and sucooling
    By jayaeros in forum Trouble Shooting
    Replies: 23
    Last Post: 05-07-2009, 06:21 AM
  5. Engineering problem? Hmmmmm
    By bernie in forum Trouble Shooting
    Replies: 71
    Last Post: 26-06-2002, 03:52 PM