    Air Volume & Ref Cap



    Size of Coldstore 46.2 x 11.6 x 16mH. Room temp +2 deg C.
    I'm using 5 x Guentner evaporator GHF050.1E/47-ES.
    Air volume of each unit cooler is 25760 m3/h. Q is 46.3 kW @ -8 deg C/ 45 deg C SST/ SCT.

    Volume of room 8575 m3.

    Can someone offer some suggestion on how much air volume should unit cooler per cubic room size.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Air Volume & Ref Cap

    Size of Coldstore 46.2 x 11.6 x 16mH.
    Is the room really 16m high?

  3. #3
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: Air Volume & Ref Cap

    What's that 16 m , that more than a 5 stories heigh . . . .
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Air Volume & Ref Cap

    Nearly 50 ft Botrous

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Air Volume & Ref Cap

    The biggest freezer we did was +/- 60 x 30 x 11 m.

    Kevin, you don't have to worry about the needed air volume versus the volume of the room.
    You calculated the needed capacity and installed it. The manufacturer of the evaporators has done his job and limited the airflow over the evaporator coil to avoid water blowing of the coil.
    What we do if we need more air circulation like you find in a blast freezer, blast chiller or in the larger fresh meat storehouses when they enter the fresh carcasses is mounting some additional room ventilation with axial fans.

    Especially because you're room is evry high, I should look if you don't have stratification of the air (different temperature layers in the height)
    You could install on the opposite side of the evaporators fans which are blowing downwards.

    Are the stored products fresh products who needs some basic minimum air circulation and are they brought in the room already at room conditions.

    I suppose they also installed very high racks in it - maybe automatically controlled sliding racks - so you could think of blowing the wind in the open spaces between the racks.
    We installed in a freezer the evaporators lined up with the open spaces between the racks so that the air blows in this open spaces.

    Install some thermometers and verify if you have stratification and if so, adjust the bulb of the temperature controller.

    I will have a look in some industrial Refrigeration books I have tomorrow and if I find something about this topic, I will post it.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: Air Volume & Ref Cap

    Quote Originally Posted by frank
    Nearly 50 ft Botrous
    I know frank , i was just comparing the 16 m to a building height
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  7. #7
    Join Date
    Jul 2005
    Location
    Malaysia
    Age
    44
    Posts
    66
    Rep Power
    19

    Re: Air Volume & Ref Cap

    Dear all,

    Yup, the height is 16 m. However, i'll discuss with the owner reg the possibitily of reducing the height to around 12 ft [40 ft] due to constraint in transporting insulation panel. In Malaysia, normally we do 40 ft height max.

    Thanks for your advise Peter, air streamer would definitely be used to reduce turbulence of air. As I'm using 5 unit blowers, i'm thinking to install the unit coolers 3 on left and 2 on right panel, staggered. Do you think it can improve air ventilation and reduce hot air pocket? And by this, 2 main line [suction & liquid] would be run. 5 blowers shall have individual thermostat that linked to one pc gateway for control and monitoring.

    I'm in fact thinking bout defrosting of the system. 3 x 60 Hp screw compressors would be used. In this scenario, how do you guys suggest defrosting be done. Is there better ways to electrically defrost it not in same time? Guess not right...Pretty heavy starting current...

Similar Threads

  1. about the refrigerant fill amount
    By hammurabi in forum Refrigeration Books
    Replies: 12
    Last Post: 31-07-2006, 10:24 AM
  2. Volume ratio selection
    By rosetennis in forum Industrial Compressors
    Replies: 4
    Last Post: 14-07-2006, 02:10 AM
  3. Co2 System Design
    By Brad Chen in forum Supermarket Refrigeration
    Replies: 5
    Last Post: 18-05-2006, 12:21 PM
  4. Information request
    By Student Eng in forum Air Conditioning
    Replies: 17
    Last Post: 21-02-2006, 12:06 PM
  5. Compressor's volume efficiency
    By John McGru in forum Fundamentals
    Replies: 0
    Last Post: 16-02-2004, 08:44 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •