Thread: Condenser Fan Motors
-
13-11-2010, 06:32 AM #1
Condenser Fan Motors
Recently went to a service call.
Complaint was that the temperature rose for a short time in a server room. served by a Roof top unit. then it returned to normal. i checked the unit over and found nothing wrong.
I found the thermostat needed recalibrating. and thought that was it.
our service manager got called out to the site again and found the condenser fan motor was failing.
I shook the shaft when i was there and felt no side to side motion. and i checked the amps. all OK. Contactor fine. fan cycling control good working order.
What other checks should i have done on the condenser fan motor?
-
13-11-2010, 07:31 AM #2
Re: Condenser Fan Motors
If the fan motor is OK, i would check whatever starts it, any kind of pressure control.
could be a faulty contact.
-
15-11-2010, 12:30 AM #3
Re: Condenser Fan Motors
have come across a similar scenario,found that run capacitor mfd value was down after seeing the current draw and the blade stalling in a good northerly wind
mmm to beer or not to beer...........lets drink breakfast
-
15-11-2010, 07:22 AM #4
Re: Condenser Fan Motors
Yeah, the capacitor is the most probable cause.
-
15-11-2010, 02:07 PM #5
Re: Condenser Fan Motors
hi , did you spin the shaft , was it spinning freely < is there any oil or greece points? what where the running amps? on most small fan motors its difficult to take a reading I have seen when the amps have to be taken on a new live cable by wrapping it 10 times around the amp meter prongs to give a true reading. all the best , sedgy
Similar Threads
-
oversizing condenser fan motors?
By delta T in forum ElectricalReplies: 3Last Post: 14-07-2010, 04:58 AM -
oversizing condenser fan motors?
By delta T in forum Chit Chat & Service StoriesReplies: 5Last Post: 13-07-2010, 02:20 PM -
How to measure COP (evaporative condenser)
By Juho in forum Technical DiscussionsReplies: 5Last Post: 04-06-2010, 07:08 PM -
Evaporative Condenser system COP
By Juho in forum CommercialReplies: 0Last Post: 03-06-2010, 09:23 AM -
Air Cooled Condenser Leakage Problem with R-404A
By RADHAKRISHNARAO in forum Technical DiscussionsReplies: 19Last Post: 30-07-2008, 12:21 PM