    Condenser Fan Motors



    Recently went to a service call.

    Complaint was that the temperature rose for a short time in a server room. served by a Roof top unit. then it returned to normal. i checked the unit over and found nothing wrong.

    I found the thermostat needed recalibrating. and thought that was it.

    our service manager got called out to the site again and found the condenser fan motor was failing.

    I shook the shaft when i was there and felt no side to side motion. and i checked the amps. all OK. Contactor fine. fan cycling control good working order.

    What other checks should i have done on the condenser fan motor?



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Condenser Fan Motors

    If the fan motor is OK, i would check whatever starts it, any kind of pressure control.
    could be a faulty contact.

  3. #3
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Condenser Fan Motors

    have come across a similar scenario,found that run capacitor mfd value was down after seeing the current draw and the blade stalling in a good northerly wind
    mmm to beer or not to beer...........lets drink breakfast

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Condenser Fan Motors

    Yeah, the capacitor is the most probable cause.

  5. #5
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Condenser Fan Motors

    hi , did you spin the shaft , was it spinning freely < is there any oil or greece points? what where the running amps? on most small fan motors its difficult to take a reading I have seen when the amps have to be taken on a new live cable by wrapping it 10 times around the amp meter prongs to give a true reading. all the best , sedgy

Similar Threads

  1. oversizing condenser fan motors?
    By delta T in forum Electrical
    Replies: 3
    Last Post: 14-07-2010, 04:58 AM
  2. oversizing condenser fan motors?
    By delta T in forum Chit Chat & Service Stories
    Replies: 5
    Last Post: 13-07-2010, 02:20 PM
  3. How to measure COP (evaporative condenser)
    By Juho in forum Technical Discussions
    Replies: 5
    Last Post: 04-06-2010, 07:08 PM
  4. Evaporative Condenser system COP
    By Juho in forum Commercial
    Replies: 0
    Last Post: 03-06-2010, 09:23 AM
  5. Air Cooled Condenser Leakage Problem with R-404A
    By RADHAKRISHNARAO in forum Technical Discussions
    Replies: 19
    Last Post: 30-07-2008, 12:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •