    Mitsubishi heat pump - advice for use in heating mode



    Hi,

    I am in the filed of BMS and controls and so my knowledge of heat pumps is limited. I'd be very greatful if anyone could assist with my query.

    Background info:
    A site I am working on currently has a number of AHUs which serve different areas. Each of these has a Mistubishi PR-20YC heat pump (currently used for cooling only but capable of heating according to Mistu literature). There is also an LPHW coil on the AHUs to provide heating when required. The supply air setpoint is 20degC. The LPHW heating is disabled when the outside air temp exceeds 17degC.

    The question:
    This heat pump is capable of being used in a heating mode. At what conditions will the heat pump be more efficient for use in heating mode than using the LPHW coil?

    My idea:
    I am considering setting up some kind of control whereby the LPHW coil will be used in cold weather up until the outside air temp reaches say, 15degC (as a rough estimate). The LPHW will then be disabled and the heat pump will then take over to provide heating until the outside air temperature reaches 17degC at which point all heating will be disabled. Does this sound like a sensible routine to implement?

    Cheers

    Rob



  2. #2
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Mitsubishi heat pump - advice for use in heating mode

    Mitsubishi Electric PR-20YC

    I think this unit is about 10 years old
    Refrigerant R22
    Single package roof top unit
    Cooling only
    20 HP about 50kw cooling

    If it was a heat pump it would have been PRH-20YA or PRH-20YA-L

    H = heat pump

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Mitsubishi heat pump - advice for use in heating mode

    There you go, fair idea let down by having the wrong kit.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    many_methods's Avatar
    many_methods Guest

    Re: Mitsubishi heat pump - advice for use in heating mode

    Aha, very interesting. Thanks very much for the info and despite being a bit disappointing this has saved me a lot of potential aggro!

    Appreciate the prompt response.

    Many thanks,

    Rob

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Vrv
    By tgoonter in forum Air Conditioning
    Replies: 4
    Last Post: 11-01-2011, 06:25 AM
  3. Ruud heat pump blower and heat problem
    By Jenkins58 in forum Heat Pumps
    Replies: 2
    Last Post: 18-02-2010, 07:04 PM
  4. Heating garage with regrigerator heat pump
    By Marks heater in forum Fundamentals
    Replies: 4
    Last Post: 11-05-2009, 02:37 AM
  5. mitsubishi heat pump
    By Mark in forum Air Conditioning
    Replies: 4
    Last Post: 17-01-2004, 10:43 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •