09-11-2010, 10:52 AM #1
Im having a problem with a Sabroe SMC108. When i try to run it will load every head but the 75%. This problem seems to have started since i removed all heads and liners,and changed discharge and suction valves on all liners. I have changed the solenoid coil,and taken the solenoid assembly apart to check for any blockages and found nothing. Also have taken the head and cylinders out to check the mechanical side of the loading gear and all seems to be fine. All pressures are fine,and motor current is fine too. So nothing appears to be wrong with the control circuit side of things. When re inserting the liner i put the loading gear in the correct load position,then once in place loading gear went back into unload position and i could see the valve inside cylinders moving to correct position. I cant think of any reason why it will not load?
09-11-2010, 11:41 AM #2
09-11-2010, 11:44 AM #3
Re: Sabroe SMC108 loading fault
gibbo88 I assume before you put head on you instal plug & force unloader gear to loaded position ?
If you do not ,unloader pins can jam in vertical position when head is installed .
Also double check both liners suction valves are free to move up & down all the way round in each cylinder liner .
If you are checking that unload mechanism is moving up & down freely , also observe when loading cylinders with plug that after valve seats that you can still screw in plug a bit more .
Did you check bumper clearance & have to adjust , or put same gaskets back in under liners?
09-11-2010, 01:04 PM #4
09-11-2010, 01:05 PM #5
when i installed liners* not head
09-11-2010, 02:03 PM #6
Gibbo88,
I'm sorry but I couldn't understood the symptoms: The frame load mechanism gets ON and then is unloaded immediately again?
Sorry about my persistence.To make progress is never good enough, I want to do better and better and better
09-11-2010, 05:58 PM #7
Hi Gibbo.
Ranger has his finger on the issue as far as I am concerned.
Forgive me for asking what may well be basic questions to you.
But as you say your problems only started after a overhaul.
So it is only fair to assume it is something you have done?
How you answer could be the crux of the problem.
Oh! also what is the oil pressure indicated when this comp is running?
Cheers Grizzly
09-11-2010, 08:38 PM #8
Not sure what you mean here but unloaders should be forced & held in the loaded position with plug when installing head .
Bumper clearance is 0.6 to 1 mm using dial indicator & magnetic stand again unloader gear has to forced into loaded condition .
Minimum oil pressure 3.5 bar
Normal oil pressure 4.5 bar
09-11-2010, 09:09 PM #9
I am wondering whether the plug has been unscrewed prior to bolting the head back into place?
Gibbo does not seem to want to answer.
10-11-2010, 04:43 AM #10
Grizzly the first Sabroe I ever did I didn't know about plugs screwed in for mounting heads .
Was lucky enough for them to be ok .
When each bank loaded it went bang so liners then seated etc .
How I didn't do any damage I'll never know .
Same machines (on R22 steel pipe) had high discharge temps after 6 months .
Pulled off heads & found bits of hard type curved square wire .
Found out eventually that discharge valve plates had worn completely through due to pipe dust & scale grinding away.Last edited by RANGER1; 10-11-2010 at 04:45 AM.
10-11-2010, 07:40 PM #11
Hi Ranger.
Nobody had fitted commissioning socks then?
I have seen the damage the huge amounts of carbon Dust / Grit that is created can cause.
Especially if the plant is on Ammonia and mineral oil.
Fortunately for me I had a older guys to learn from.
So I was spared the trauma of not setting the loading gear correctly.
I suspect "we / you have gotten to near the truth and Gibbo has done a runner?
Gibbo, take note the good engineers admit they make mistakes.
No-one with half a brain is going to criticise we all make mistakes.
Simply with time, the number you make grow smaller.
Hopefully anyway.
I learnt a brilliant Australian saying the other day my friend, FIGJAM.
I can relate to this. If you know what i mean.
How about you
22-11-2010, 07:32 PM #12
unscrew the plug and measure the actual oilpressure in the servocylinder solenoidvalves do go bad.
but then again if it's after an overhaul the most likely cause is assembling it the wrong way the plug is the Father the holy spirit and the son when it comes to overhaul the SMC
vrv3 au fault
By transit 1 in forum Air ConditioningReplies: 6Last Post: 04-11-2010, 10:19 PM -
Mitsubishi 1500 fault code fault
By pie man in forum Air ConditioningReplies: 9Last Post: 06-05-2010, 09:30 PM -
Supra common fault - usually misdiagnosed.
By carrier_trained in forum TransportReplies: 3Last Post: 15-04-2010, 08:56 PM -
Fault with Tango cassette
By airefresco in forum Air ConditioningReplies: 8Last Post: 19-09-2007, 08:42 AM -
UA Daikin Fault Code
By jedi in forum Air ConditioningReplies: 2Last Post: 23-07-2007, 01:44 PM