    I had problems with the oil temperature of this equipment is a system that uses ammonia and serves as a chiller I leave the machine operating data before protected.
    100% capacity
    2.20 volume
    37.5 psig suction pressure
    temperature 10.8 ° C
    15.4 ° C superheat
    133.4 psig discharge pressure
    temperature 86.2 ° c
    60.6 ° C superheat
    oil pressure 130 psig
    temperature 73.7 ° c
    process temperature 11.5 ° C
    10.0 ° C setpoint
    12.0 ° c boot
    unemployment 9.0 ° c
    I hope their comments and their help
    Oct 2007
    argentina
    Re: frick RXF-39H
    hi, you have too high suction superheat, try to less it.
    Nov 2004
    China
    176
    Re: frick RXF-39H
    Agree with ping. If this is a flooded chiller the superheat should be almost 0. What is the oil cooling method?
    Oct 2009
    merida mexico
    282
    15
    Re: frick RXF-39H
    oil cooling is liquid (eazycool), the evaporator is flooded and even goes ahy heat exchanger
    Oct 2009
    67
    28
    Re: frick RXF-39H
    What is the oil high temp set point?
    Oct 2009
    merida mexico
    282
    15
    Re: frick RXF-39H
    167°f cout uot hig oil temp
    Jul 2007
    Czech
    61
    373
    Re: frick RXF-39H
    Can Cooler - ammonia with oil? compressor is in good condition? does not vibrate? noise?
    Oct 2009
    merida mexico
    282
    15
    Re: frick RXF-39H
    josef
    the compressor is new, operating at 100% increases the temperature, ammonia, oil is cooled by liquid injection, and the evaporator is flooded, we used as chiller
    Jul 2007
    Czech
    61
    373
    Re: frick RXF-39H
    Insuffi cient liquid supply. Check receiver level. Check strainer.
    Suction superheat too high. Correct system problem.
    Liquid strainer blocked. Clean strainer.
    Operating conditions signifi cantly different from design.
    Malfunctioning Vi Control Solenoids. See function check of the compressor
    "Volumizer II Vi Control" for further detail.
    Check motor valve operation and calibration.
    Check calibration of analog output.
    Oct 2009
    merida mexico
    282
    15
    Re: frick RXF-39H
    ok, the calibration of the valve and was verified, the correct operating saw and automatic way, I amtenido the compressor at 85% capacity and works well, the liquid level is 3 peephole in the entrance of liquid and 2 in the evaporator
    Jul 2007
    Czech
    61
    373
    Re: frick RXF-39H
    Volume goes 2.2 to 5?
    Oct 2009
    merida mexico
    282
    15
    Re: frick RXF-39H
    yes. cleaning strainer succion,liquid inyection.return oi strainer
    Oct 2009
    merida mexico
    282
    15
    Re: frick RXF-39H
    are in fact three compressors Frick and only protects the new
    Jul 2007
    Czech
    61
    373
    Re: frick RXF-39H
    Check your email
    Oct 2009
    merida mexico
    282
    15
    Re: frick RXF-39H
    josef:
    thanks
    Auckland
    74
    3,357
    37
    Re: frick RXF-39H
    The liquid injection is too low, check expansion control and receiver supply levels.
    Oct 2009
    merida mexico
    282
    15
    Re: frick RXF-39H
    the injection of liquid is a electronic valve
    Jul 2007
    Czech
    61
    373
    Re: frick RXF-39H
    The compressor is new or overhaul?
    I think your problem is the compressor.
  19. #19
    Oct 2009
    merida mexico
    282
    15
    Re: frick RXF-39H
    compressor is new.lo've been working at 90% maximum load
  20. #20
    3,357
    Re: frick RXF-39H
    serviceman ,
    If you have liquid injection discharge temp & oil temp should be same .
    What is the liquid injection set point ?
    I would have thought between 130 -140 f .
    Sensor should be on ideally discharge line out of compressor .
    As everyone also suggests good liquid reciever levels.
    Also oil injection into rotors must be adequate to assist cooling of compressor as not enough may cause rotor damage .
  21. #21
    Jul 2007
    Czech
    61
    373
    Re: frick RXF-39H
    Thank serviceman, so you have a compressor problem. Calibration, capacity control, perhaps from the production.
  22. #22
    Oct 2009
    merida mexico
    282
    15
    Re: frick RXF-39H
    thanks josef
  23. #23
    Jul 2007
    Czech
    61
    373
    Re: frick RXF-39H
    Do not write more?
  24. #24
    Jun 2009
    Canada
    55
    82
    15
    Re: frick RXF-39H
    Have you verified that the main oil injection orifice is the correct size? Sounds like the orifice is too small. Frick usually sends a package of different sized orifices with new compressors. I've had to change several of these.
    C Ice
  25. #25
    Oct 2009
    merida mexico
    282
    15
    Re: frick RXF-39H
    When the package arrived only brought hand cooling, oil filter and oil. holes will have a picture?
  26. #26
    Jul 2008
    Houston Tx
    42
    Re: frick RXF-39H
    There is a 7 turn valve that should have a yellow cap on it. If that valve is not set correctly that could also affect your oil and discharge temps
  1. Frick suction check failure
    By CanadianIce in forum Industrial Compressors
    Last Post: 08-04-2010, 11:43 AM
  2. Frick IOMM
    By NH3ISFORME in forum Industrial Compressors
    Last Post: 03-03-2010, 01:46 PM
  3. problem with volume on frick screw compressor
    By samlee12 in forum Industrial
    Last Post: 29-10-2009, 06:06 AM
  4. problem with frick screw volume
    By samlee12 in forum Industrial Compressors
    Last Post: 20-06-2009, 02:46 PM
  5. Replies: 12
    Last Post: 16-06-2008, 10:06 AM