04-11-2010, 08:52 PM #1
frick RXF-39H
I had problems with the oil temperature of this equipment is a system that uses ammonia and serves as a chiller I leave the machine operating data before protected.
100% capacity
2.20 volume
37.5 psig suction pressure
temperature 10.8 ° C
15.4 ° C superheat
133.4 psig discharge pressure
temperature 86.2 ° c
60.6 ° C superheat
oil pressure 130 psig
temperature 73.7 ° c
process temperature 11.5 ° C
10.0 ° C setpoint
12.0 ° c boot
unemployment 9.0 ° c
I hope their comments and their help
-
05-11-2010, 12:17 AM #2
Re: frick RXF-39H
hi, you have too high suction superheat, try to less it.
-
05-11-2010, 09:45 AM #3
Re: frick RXF-39H
Agree with ping. If this is a flooded chiller the superheat should be almost 0. What is the oil cooling method?
-
05-11-2010, 02:14 PM #4
Re: frick RXF-39H
oil cooling is liquid (eazycool), the evaporator is flooded and even goes ahy heat exchanger
-
16-11-2010, 06:02 PM #5
Re: frick RXF-39H
What is the oil high temp set point?
-
23-11-2010, 03:00 PM #6
Re: frick RXF-39H
167°f cout uot hig oil temp
-
23-11-2010, 04:22 PM #7
Re: frick RXF-39H
Can Cooler - ammonia with oil? compressor is in good condition? does not vibrate? noise?
-
23-11-2010, 05:16 PM #8
Re: frick RXF-39H
josef
the compressor is new, operating at 100% increases the temperature, ammonia, oil is cooled by liquid injection, and the evaporator is flooded, we used as chiller
-
23-11-2010, 05:40 PM #9
Re: frick RXF-39H
Insuffi cient liquid supply. Check receiver level. Check strainer.
Suction superheat too high. Correct system problem.
Liquid strainer blocked. Clean strainer.
Operating conditions signifi cantly different from design.
Malfunctioning Vi Control Solenoids. See function check of the compressor
"Volumizer II Vi Control" for further detail.
Check motor valve operation and calibration.
Check calibration of analog output.
-
23-11-2010, 06:59 PM #10
Re: frick RXF-39H
ok, the calibration of the valve and was verified, the correct operating saw and automatic way, I amtenido the compressor at 85% capacity and works well, the liquid level is 3 peephole in the entrance of liquid and 2 in the evaporator
-
23-11-2010, 07:51 PM #11
Re: frick RXF-39H
Volume goes 2.2 to 5?
-
23-11-2010, 08:13 PM #12
Re: frick RXF-39H
yes. cleaning strainer succion,liquid inyection.return oi strainer
-
23-11-2010, 08:15 PM #13
Re: frick RXF-39H
are in fact three compressors Frick and only protects the new
-
23-11-2010, 09:58 PM #14
Re: frick RXF-39H
Check your email
-
23-11-2010, 10:21 PM #15
Re: frick RXF-39H
josef:
thanks
-
23-11-2010, 11:06 PM #16
Re: frick RXF-39H
The liquid injection is too low, check expansion control and receiver supply levels.
-
24-11-2010, 02:37 PM #17
Re: frick RXF-39H
the injection of liquid is a electronic valve
-
24-11-2010, 03:10 PM #18
Re: frick RXF-39H
The compressor is new or overhaul?
I think your problem is the compressor.
-
24-11-2010, 07:30 PM #19
Re: frick RXF-39H
compressor is new.lo've been working at 90% maximum load
-
24-11-2010, 08:17 PM #20
Re: frick RXF-39H
serviceman ,
If you have liquid injection discharge temp & oil temp should be same .
What is the liquid injection set point ?
I would have thought between 130 -140 f .
Sensor should be on ideally discharge line out of compressor .
As everyone also suggests good liquid reciever levels.
Also oil injection into rotors must be adequate to assist cooling of compressor as not enough may cause rotor damage .
-
24-11-2010, 08:45 PM #21
Re: frick RXF-39H
Thank serviceman, so you have a compressor problem. Calibration, capacity control, perhaps from the production.
-
13-01-2011, 03:46 PM #22
Re: frick RXF-39H
thanks josef
-
13-01-2011, 10:07 PM #23
Re: frick RXF-39H
Do not write more?
-
17-01-2011, 04:57 PM #24
Re: frick RXF-39H
Have you verified that the main oil injection orifice is the correct size? Sounds like the orifice is too small. Frick usually sends a package of different sized orifices with new compressors. I've had to change several of these.
C Ice
-
17-01-2011, 05:51 PM #25
Re: frick RXF-39H
When the package arrived only brought hand cooling, oil filter and oil. holes will have a picture?
-
25-04-2011, 05:11 PM #26
Re: frick RXF-39H
There is a 7 turn valve that should have a yellow cap on it. If that valve is not set correctly that could also affect your oil and discharge temps
Similar Threads
-
Frick suction check failure
By CanadianIce in forum Industrial CompressorsReplies: 4Last Post: 08-04-2010, 11:43 AM -
Frick IOMM
By NH3ISFORME in forum Industrial CompressorsReplies: 2Last Post: 03-03-2010, 01:46 PM -
problem with volume on frick screw compressor
By samlee12 in forum IndustrialReplies: 4Last Post: 29-10-2009, 06:06 AM -
problem with frick screw volume
By samlee12 in forum Industrial CompressorsReplies: 9Last Post: 20-06-2009, 02:46 PM -
Ammonia Circulation rate - by Frick/ Vitler
By smpsmp45 in forum NH3Replies: 12Last Post: 16-06-2008, 10:06 AM