    Exclamation frick RXF-39H



    I had problems with the oil temperature of this equipment is a system that uses ammonia and serves as a chiller I leave the machine operating data before protected.

    100% capacity
    2.20 volume
    37.5 psig suction pressure
    temperature 10.8 ° C
    15.4 ° C superheat

    133.4 psig discharge pressure
    temperature 86.2 ° c
    60.6 ° C superheat
    oil pressure 130 psig
    temperature 73.7 ° c

    process temperature 11.5 ° C
    10.0 ° C setpoint
    12.0 ° c boot
    unemployment 9.0 ° c

    I hope their comments and their help



  2. #2
    Join Date
    Oct 2007
    Location
    argentina
    Age
    62
    Posts
    53
    Rep Power
    17

    Re: frick RXF-39H

    hi, you have too high suction superheat, try to less it.

  3. #3
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: frick RXF-39H

    Agree with ping. If this is a flooded chiller the superheat should be almost 0. What is the oil cooling method?

  4. #4
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: frick RXF-39H

    oil cooling is liquid (eazycool), the evaporator is flooded and even goes ahy heat exchanger

  5. #5
    Join Date
    Oct 2009
    Location
    USA
    Age
    67
    Posts
    28
    Rep Power
    0

    Re: frick RXF-39H

    What is the oil high temp set point?

  6. #6
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: frick RXF-39H

    167°f cout uot hig oil temp

  7. #7
    Join Date
    Jul 2007
    Location
    Czech
    Age
    61
    Posts
    374
    Rep Power
    18

    Re: frick RXF-39H

    Can Cooler - ammonia with oil? compressor is in good condition? does not vibrate? noise?

  8. #8
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: frick RXF-39H

    josef
    the compressor is new, operating at 100% increases the temperature, ammonia, oil is cooled by liquid injection, and the evaporator is flooded, we used as chiller

  9. #9
    Join Date
    Jul 2007
    Location
    Czech
    Age
    61
    Posts
    374
    Rep Power
    18

    Re: frick RXF-39H

    Insuffi cient liquid supply. Check receiver level. Check strainer.
    Suction superheat too high. Correct system problem.
    Liquid strainer blocked. Clean strainer.
    Operating conditions signifi cantly different from design.
    Malfunctioning Vi Control Solenoids. See function check of the compressor
    "Volumizer II Vi Control" for further detail.
    Check motor valve operation and calibration.
    Check calibration of analog output.

  10. #10
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: frick RXF-39H

    ok, the calibration of the valve and was verified, the correct operating saw and automatic way, I amtenido the compressor at 85% capacity and works well, the liquid level is 3 peephole in the entrance of liquid and 2 in the evaporator



  11. #11
    Join Date
    Jul 2007
    Location
    Czech
    Age
    61
    Posts
    374
    Rep Power
    18

    Re: frick RXF-39H

    Volume goes 2.2 to 5?

  12. #12
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: frick RXF-39H

    yes. cleaning strainer succion,liquid inyection.return oi strainer

  13. #13
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: frick RXF-39H

    are in fact three compressors Frick and only protects the new

  14. #14
    Join Date
    Jul 2007
    Location
    Czech
    Age
    61
    Posts
    374
    Rep Power
    18

    Re: frick RXF-39H

    Check your email

  15. #15
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: frick RXF-39H

    josef:

    thanks

  16. #16
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: frick RXF-39H

    The liquid injection is too low, check expansion control and receiver supply levels.

  17. #17
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: frick RXF-39H

    the injection of liquid is a electronic valve

  18. #18
    Join Date
    Jul 2007
    Location
    Czech
    Age
    61
    Posts
    374
    Rep Power
    18

    Re: frick RXF-39H

    The compressor is new or overhaul?
    I think your problem is the compressor.

  19. #19
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: frick RXF-39H

    compressor is new.lo've been working at 90% maximum load

  20. #20
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: frick RXF-39H

    serviceman ,
    If you have liquid injection discharge temp & oil temp should be same .
    What is the liquid injection set point ?
    I would have thought between 130 -140 f .
    Sensor should be on ideally discharge line out of compressor .

    As everyone also suggests good liquid reciever levels.
    Also oil injection into rotors must be adequate to assist cooling of compressor as not enough may cause rotor damage .

  21. #21
    Join Date
    Jul 2007
    Location
    Czech
    Age
    61
    Posts
    374
    Rep Power
    18

    Re: frick RXF-39H

    Thank serviceman, so you have a compressor problem. Calibration, capacity control, perhaps from the production.

  22. #22
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: frick RXF-39H

    thanks josef

  23. #23
    Join Date
    Jul 2007
    Location
    Czech
    Age
    61
    Posts
    374
    Rep Power
    18

    Re: frick RXF-39H

    Do not write more?

  24. #24
    Join Date
    Jun 2009
    Location
    Canada
    Age
    55
    Posts
    82
    Rep Power
    15

    Re: frick RXF-39H

    Have you verified that the main oil injection orifice is the correct size? Sounds like the orifice is too small. Frick usually sends a package of different sized orifices with new compressors. I've had to change several of these.

    C Ice

  25. #25
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: frick RXF-39H

    When the package arrived only brought hand cooling, oil filter and oil. holes will have a picture?

  26. #26
    Join Date
    Jul 2008
    Location
    Houston Tx
    Posts
    42
    Rep Power
    0

    Re: frick RXF-39H

    There is a 7 turn valve that should have a yellow cap on it. If that valve is not set correctly that could also affect your oil and discharge temps

Similar Threads

  1. Frick suction check failure
    By CanadianIce in forum Industrial Compressors
    Replies: 4
    Last Post: 08-04-2010, 11:43 AM
  2. Frick IOMM
    By NH3ISFORME in forum Industrial Compressors
    Replies: 2
    Last Post: 03-03-2010, 01:46 PM
  3. problem with volume on frick screw compressor
    By samlee12 in forum Industrial
    Replies: 4
    Last Post: 29-10-2009, 06:06 AM
  4. problem with frick screw volume
    By samlee12 in forum Industrial Compressors
    Replies: 9
    Last Post: 20-06-2009, 02:46 PM
  5. Replies: 12
    Last Post: 16-06-2008, 10:06 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •