04-11-2010, 08:10 PM #1
How to calculate Wats per sq.meter by dT
Example : heated floor surface area 100 sq.meters.lets say room height 3m, so 300 cubic meters volume of air in the room, RH=50%, florr surface temperature is 30c, desired romm temp 22c, dt=8.
Question : how to calculate energy radiated by Wats per sq.m (W/m2)
04-11-2010, 08:29 PM #2
Re: How to calculate Wats per sq.meter by dT
You are missing a vital part of the equation - TIME
Over time, the input temperature of 30C will bring the room up to 22C over TIME, providing that the heat input is greater than the heat loss.
Watts (J/S) is a measure of heat /time
04-11-2010, 08:43 PM #3
For underfloor heating the floors should not exceed 29°C but for bathrooms which are typically 33°C.
For floors the surface film heat transfer coefficient is limited to approximately 10-11W/m²K so for your 8K TD the maximum heat transfer would be 8K x 11W/m²K = 88W/m²
But you ask how much would be radiated? I'm not sure how to divide Q into radiant and convective components? I don't know the proportions - I don't think it matters, does it?