    Hello everyone,
    This is my first post, so I hope I won't be getting too much out of the subject.
    I am having trouble identifying two Sporlan expansion valves which I will be replacing with Danfoss. I have to replace with Danfoss as I have a time limit for delivering the work.
    I managed to get the tonnage for both valves except for the thermostatic charges. Would anybody be able to help me with identifying the thermostatic charges C, L and Z?
    It has already been 2 days and since I posted my request to Parker and still no reply.
    Thank you.
  2. #2
    Join Date
    Jun 2009
    Location
    Canada
    Age
    55
    Posts
    82
    Rep Power
    15
    Re: Sporlan Expansion Valve
    What temps are the evaporators operating at?
    C Ice
  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60
    Sporlan TEV documents here, see doc 10-10 and 10-9.
    EG, C charge for 50°F to -10°F
    Z charge for 0°F to -40°F
    http://www.sporlanonline.com/tevs.shtml
    Danfoss charge data
    http://www.danfoss.com/North_America...Language=en-US
    Click on type T2 / TE2 614KB.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015
  4. #4
    Join Date
    Oct 2009
    Location
    USA
    Age
    67
    Posts
    28
    Rep Power
    0
    Here is another site http://www.sporlanonline.com/
  5. #5
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20
    The L charge is temperature dependent and not so responsive to pressure change. It is intended for use in larger ammonia systems with multiple evaporators where a change in the flow through one expansion valve has almost no effect on suction pressure.
  6. #6
    Join Date
    Aug 2009
    Location
    Mauritius
    Age
    41
    Posts
    28
    Rep Power
    0
    Thanks a lot, it was for an ammonia application, but single circuit. It contained about 43 individual circuits. We had them ordered from Parker and it took about 3 months to arrive.
  7. #7
    Join Date
    Aug 2010
    Location
    USA
    Posts
    4
    Rep Power
    0
    Ashwin123,
    Do you mind giving us the details on the Parker Tx valves for ammonia?
    Happens to be that I'm looking for Tx valves to repalce old Sporlan Tx valves
    Thanks, Josue
Similar Threads
  1. Replies: 3
    Last Post: 09-05-2009, 03:17 AM
  2. Actual Expansion Valve Process
    By AastroGuru in forum Fundamentals
    Last Post: 03-02-2009, 09:53 AM
  3. Setting of Hand expansion valve
    By Iceehot in forum NH3
    Last Post: 10-09-2008, 01:25 AM
  4. the function of the electronic expansion valve
    By Crystal-426 in forum Fundamentals
    Last Post: 22-06-2008, 12:29 PM
  5. Need Divine Intervention - plugged drier or expansion valve?
    By archibaldtuttle in forum Trouble Shooting
    Last Post: 08-06-2008, 06:52 PM
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts