    Hi everybody!
    Please, tell me
    is there any method to find out R407С condition in refrigeration circuit? If one of the components is lost, ***** changed its properties. But I am not sure about leak! How can it be checked?
    Last edited by chillin out; 23-07-2010 at 06:06 PM.



  2. #2
    Join Date
    Aug 2008
    Location
    London
    Age
    42
    Posts
    55
    Rep Power
    16

    Re: R407C leaked or not?

    Hello there,

    The best way to check the composition of the refrigerant is to use a refrigerant analysis kit from BOC, They send you a cylinder which you recover from chiller circuit approx 150-300 grams and send back to BOC, they produce report for you which confirms moisture non condensibles and composition.

    Hope this helps!

    regards Wilko

  3. #3
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: R407C leaked or not?

    have tryed using a comparator

  4. #4
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: R407C leaked or not?

    Quote Originally Posted by AndRay1975 View Post
    Hi everybody!
    Please, tell me
    is there any method to find out R407С condition in refrigiration circuit? If one of the components is lost, ***** changed its properties. But I am not sure about leak! How can it be checked?

    The standing pressure should be what it says on your chart for the given temp, if ok.

    The only accurate way would be to send a sample off for testing.

    taz

    .

  5. #5
    Join Date
    Sep 2010
    Location
    india
    Age
    38
    Posts
    4
    Rep Power
    0

    Re: R407C leaked or not?

    sir what is the actual running parameter of air cooled DX air conditioning system with 407c refrigerant,,,please help

  6. #6
    Join Date
    Feb 2010
    Location
    Ireland
    Age
    38
    Posts
    82
    Rep Power
    15

    Re: R407C leaked or not?

    Yellow jacket do a gas analiser. Have not tried it but it might be worth a look.

  7. #7
    Join Date
    May 2008
    Location
    Malta
    Age
    68
    Posts
    67
    Rep Power
    16

    Re: R407C leaked or not?

    What makes you suspect a leak,please supply pressures high and low and visual condition of pipework condenser and evap and temperatures.If analysis of the gas is not available where you live the best thing to do is recover the refrigerant weigh it and compare to the stated charge weight if less you have a leak.Pressurize the system not greater than the stated test pressure with a trace of refrigerant and test for leaks repair it and evacuate to 500 microns using an accurate vacuum gauge leave standing for 24hrs if it held charge to the specified weight with virgin gas if not you still have a leak if the pressure increases slightly then you need to evacuate further as there is still moisture.I hope this helps you

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: R407C leaked or not?

    If the leak happened in any part where the refrigerant is one phase (superheated or subcooled), then composition remains constant.
    Composition shifts only when refrigerant is lost in 2-phases equilibrium.

  9. #9
    R031's Avatar
    R031 Guest

    Re: R407C leaked or not?

    Quote Originally Posted by AndRay1975 View Post
    Hi everybody!
    Please, tell me
    is there any method to find out R407С condition in refrigeration circuit? If one of the components is lost, ***** changed its properties. But I am not sure about leak! How can it be checked?
    If You are not sure about leak do the recover of the gas on the scale , and if the measurements nearly equall as it is on the board (5%)then R407 is still good but if leak was bigger than 10% you must change (refill) the gas!

  10. #10
    Join Date
    Oct 2010
    Location
    flitwick
    Age
    40
    Posts
    12
    Rep Power
    0

    Re: R407C leaked or not?

    Quote Originally Posted by R031 View Post
    If You are not sure about leak do the recover of the gas on the scale , and if the measurements nearly equall as it is on the board (5%)then R407 is still good but if leak was bigger than 10% you must change (refill) the gas!
    Slightly off topic, i am aware of the 10% factor with R407c however i have been quoted different percentages from various people in the industry. Could you copy a link to the documentation regarding the 10% factor?

    Thank you

  11. #11
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: R407C leaked or not?

    It's a common mistake to consider a leakage from a refrigerant circuit like a distillation process.
    If the leak is on the vapour side §(single phase), than all components are lost in the same percentage.
    Distillation only happens when the liquid evaporates at an intermediate temperature between the bubble and dew temperature for that pressure, which is highly unlikely.

    As a side note: if it was that simple to distillate, then why building oil refineries?

Similar Threads

  1. r407c
    By dunny123 in forum Air Conditioning
    Replies: 3
    Last Post: 21-07-2009, 08:44 AM
  2. EVAPORATOR leaked
    By James priyono in forum Air Conditioning
    Replies: 4
    Last Post: 23-05-2009, 10:19 AM
  3. r407c chiller issue
    By Lc_shi in forum New Technologies
    Replies: 3
    Last Post: 09-01-2008, 01:22 AM
  4. R22 vs R407C.....................again!!
    By Abe in forum Air Conditioning
    Replies: 5
    Last Post: 24-07-2003, 12:21 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •