23-07-2010, 01:15 PM #1
Hi everybody!
Please, tell me
is there any method to find out R407С condition in refrigeration circuit? If one of the components is lost, ***** changed its properties. But I am not sure about leak! How can it be checked?Last edited by chillin out; 23-07-2010 at 06:06 PM.
-
23-07-2010, 01:56 PM #2
Re: R407C leaked or not?
Hello there,
The best way to check the composition of the refrigerant is to use a refrigerant analysis kit from BOC, They send you a cylinder which you recover from chiller circuit approx 150-300 grams and send back to BOC, they produce report for you which confirms moisture non condensibles and composition.
Hope this helps!
regards Wilko
-
23-07-2010, 02:10 PM #3
Re: R407C leaked or not?
have tryed using a comparator
-
23-07-2010, 02:18 PM #4
-
15-09-2010, 11:17 AM #5
Re: R407C leaked or not?
sir what is the actual running parameter of air cooled DX air conditioning system with 407c refrigerant,,,please help
-
15-09-2010, 02:51 PM #6
Re: R407C leaked or not?
Yellow jacket do a gas analiser. Have not tried it but it might be worth a look.
-
15-09-2010, 04:19 PM #7
Re: R407C leaked or not?
What makes you suspect a leak,please supply pressures high and low and visual condition of pipework condenser and evap and temperatures.If analysis of the gas is not available where you live the best thing to do is recover the refrigerant weigh it and compare to the stated charge weight if less you have a leak.Pressurize the system not greater than the stated test pressure with a trace of refrigerant and test for leaks repair it and evacuate to 500 microns using an accurate vacuum gauge leave standing for 24hrs if it held charge to the specified weight with virgin gas if not you still have a leak if the pressure increases slightly then you need to evacuate further as there is still moisture.I hope this helps you
-
15-09-2010, 04:46 PM #8
Re: R407C leaked or not?
If the leak happened in any part where the refrigerant is one phase (superheated or subcooled), then composition remains constant.
Composition shifts only when refrigerant is lost in 2-phases equilibrium.
-
27-09-2010, 07:15 PM #9
-
02-11-2010, 09:26 PM #10
-
03-11-2010, 08:54 AM #11
Re: R407C leaked or not?
It's a common mistake to consider a leakage from a refrigerant circuit like a distillation process.
If the leak is on the vapour side §(single phase), than all components are lost in the same percentage.
Distillation only happens when the liquid evaporates at an intermediate temperature between the bubble and dew temperature for that pressure, which is highly unlikely.
As a side note: if it was that simple to distillate, then why building oil refineries?
Similar Threads
-
r407c
By dunny123 in forum Air ConditioningReplies: 3Last Post: 21-07-2009, 08:44 AM -
EVAPORATOR leaked
By James priyono in forum Air ConditioningReplies: 4Last Post: 23-05-2009, 10:19 AM -
r407c chiller issue
By Lc_shi in forum New TechnologiesReplies: 3Last Post: 09-01-2008, 01:22 AM -
R22 vs R407C.....................again!!
By Abe in forum Air ConditioningReplies: 5Last Post: 24-07-2003, 12:21 AM