Results 1 to 12 of 12
    Aug 2009
    Singapore
    47
    42
    Reasons for Chiller Surge
    Dear All,
    I'like to know what are the reasons to cause surging on water cooled centrifugal chillers?
    Thanks.
    Dec 2008
    Portugal
    48
    1,020
    Re: Reasons for Chiller Surge
    I suppose that on of the reasons could be the high condensing pressure causing the "stal".
    Mar 2006
    Merate (LC) - Italy
    2,549
    Operation out of the envelope.
    Oct 2010
    Greece
    52
    97
    14
    Hi KSM,
    Each centrifugal compressor has a maximum lift.(HP-LP difference)
    This lift vary depending on IGV position.
    When the compressor is forced to exceed the maximum lift then the discharge pressure goes from discharge to suction.
    When the lift goes bellow maximum then the gas flows again from suction to discharge.
    This dangerous operation is called surge. (Operation out of compressor map)
    Possible surge causes are:
    Poor water flow in condenser.
    Poor water flow in evaporator.
    Scaled condenser.
    Scaled evaporator.
    Low refrigerant charge.
    Combination of all above.
    No condensable gas in refrigerant.
    Bad refrigerant quality.
    And many other causes depending on design (unit design / piping design) in case of a new chiller / new installation.
    Jun 2008
    TURKMENISTAN
    44
    14
    u can find good information in this document. hope it will help u...
    h t t p
    w
    w
    w .
    mcquay .
    com /
    mcquaybiz /
    literature /
    lit_corporate /
    AppGuide /
    AG_31_002 .
    pdf
    excuseme ı dont have enough message i couldnt write the link correctly. u can delete the space by this way u can find the document.
    Oct 2008
    mallorca, spain,
    75
    768
    hi ksm, is the centrif loading too fast?
    Split Croatia
    57
    6,151
    36
    I would like to know what you mean by "surging" and who (and why) made that judgment.
    Aug 2009
    Singapore
    47
    42
    Dear Nike,
    The sound comes out from Chiller is like Elephant squealing sound and the Ampere readings from Analogue Ampere Meter also unstable.So i thaught that is Chiller Surging.
    Please correct me if i wrong.Thanks.
    Aug 2009
    Singapore
    47
    42
    No Sedgy.Chiller is not loading too fast.Thanks.
    Aug 2009
    Singapore
    47
    42
    Thanks All.
    Apr 2009
    israel
    778
    Quote Originally Posted by ksm View Post
    Dear Nike,
    Hi:
    it would appear that you are correct and the sound you are hearing is indeed a surge condition.
    this is mostly caused by either very low demand and low condensing water temp,or very high condensing water temp .
    and many more abnormal conditions.
    this condition is not good for the unit and will eventully leed to catastrophical failure!!!!
    it would be advised to control your condensing water temp and monitor the control of your loading .
    most units have a protection that senses a surge condition and will stop the machine.
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
    Aug 2009
    Singapore
    47
    42
    Thanks a lot.
  1. Replies: 1
    Last Post: 23-03-2010, 08:15 PM
  2. Inline surge protector
    By wilson77 in forum Air Conditioning
    Last Post: 20-11-2009, 12:58 AM