18-07-2005, 11:45 PM #1
R407 refrigerant
I have installed Hitachi heatpumps in my home in Brazil which use R407. The contractor is having difficulty charging the R407 so that the pressurestat protection devices do not kick out the compressors. In heating mode, with normal charge the suction pressure drops below 25PSI when temperatures are below 5C. If he adds refrigerant so this does not happen, on warmer days above 15C, the pressure exceeds the top limit of 450PSI. What are the normal operating limits for R407 in both heating and cooling modes? Is R407 commonly used? I do not know whether it is A, B or C.
-
19-07-2005, 07:13 AM #2
Re: R407 refrigerant
First of all find some one who knows what they are doing, secondly, remove all the gas in an environmentally friendly manner, dehydrate the system, weigh in a fresh charge as detailed on the data plate, work out how metres of pipe you have and add the required gas per metre. It should then work perfectly, if it doesn't you have a problem elsewhere. Don't forget to weigh the gas in in the liquid phase and not vapour, use new gas not reclaimed or recycled, surely your "contractor" knows all this any way, if he doesn't he should not be messing.
-
19-07-2005, 07:36 PM #3
Re: R407 refrigerant
Originally Posted by JCole21961
If you are not careful you will end up with a U/S compressor (no, that's not one made in America)
-
19-07-2005, 08:07 PM #4
Re: R407 refrigerant
most hitarchi units come in england pre loaded with 10m worth of gas depending on model we add approx .19kg per metre over 10m.
-
19-07-2005, 11:23 PM #5
Re: R407 refrigerant
It gets you worried, doesn't it Frank ??
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
20-07-2005, 12:12 AM #6
Re: R407 refrigerant
You'll need abot 4.5 to 5.0 bar suction pressure.
-
21-07-2005, 02:21 AM #7
Re: R407 refrigerant
Thanks. What are the normal upper and lower pressure values for R407 under the normal extremes of weather in heating and cooling mode? I have read in another report that R407 is about 40% less efficient than R22 in cooling mode. Is this true?
-
21-07-2005, 08:04 PM #8
Re: R407 refrigerant
I have read in another report that R407 is about 40% less efficient than R22 in cooling mode. Is this true?
-
28-08-2005, 11:30 PM #9
Re: R407 refrigerant
Hello Frank! They are now designing evaporators which are better suited to R407c's glide and they can actually benefit from it! But still, when all is taken into consideration, they are'nt as efficient as an azeotropic blend.
j p g
-
29-08-2005, 03:34 PM #10
Re: R407 refrigerant
Hi Brian
Did you get my e-mail?
R407C? - Its getting to be old hat now
-
29-08-2005, 05:25 PM #11
Re: R407 refrigerant
We need model numbers of both the indoor and outdoor unit, The size pipe you have used and the pipe run distance (one way).
Hitachi utopia units are fantastic and always work when installed correctly (well almost always)
Its imperative that the charge is correct, For this you need to dehydrate, and weigh in the correctly calcul;ated charge.
I'll post the correct weight of R407c if you post the details I have asked for.
As already mentioned you need to charge in liquid phase. And make sure you are experianced in refrigeration or ac, if not you should get an engineer in otherwise i dont hold out much hope of the system surviving much more abuse.
Similar Threads
-
R600 Refrigerant.
By tonydeith in forum RefrigerantsReplies: 14Last Post: 21-04-2011, 08:52 AM -
CARE refigerants by BOC
By dogma in forum RefrigerantsReplies: 8Last Post: 23-03-2010, 12:39 PM -
Best way to sense level of liquid refrigerant in receiver?
By star882 in forum FundamentalsReplies: 2Last Post: 16-11-2005, 05:34 PM -
Refrigerant Reclamation
By herefishy in forum CommercialReplies: 6Last Post: 23-07-2003, 08:19 AM -
Which refrigerant to use for low temp apps?
By DaBit in forum Technical SpeculationsReplies: 14Last Post: 21-09-2002, 03:17 PM