    Useing a 407C comp for R22 app?



    Ive got a lofty style system that is on R22 and its just droped its compressor! Its a Lunite Rotary, problem is that it seems they dont make them any more but point you towards the R407c version which is the same in displacement and body size but in its data surgests it has a slightly lower duty ( im guessing this is due to the different gas its for).

    So im wondering can i just use the 407c version and fill it with R22r or will i need to convert the system to 407c wich im assumeing will be a pain in the ass as its a cap tube system?

    Cheers,

    Greg



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Useing a 407C comp for R22 app?

    I don't see a problem with running a R407C comp on R22, the oil is compatable and i expect the compressor is pretty much the same internally.

    I have a lot of R404A comps running on R22 on dairy stuff, in fact i would fit them even if a R22 one is still available as it may help with later refrigerant replacements when R22 get hard to get.

  3. #3
    Join Date
    Oct 2010
    Location
    INDIA
    Posts
    5
    Rep Power
    0

    Re: Useing a 407C comp for R22 app?

    hi you actually need to check with compressor manufacturer as compressors made by hitachihas the compatibilty to use both refrigerants but all all compressors

  4. #4
    Join Date
    Jun 2009
    Location
    East Anglia
    Age
    38
    Posts
    204
    Rep Power
    15

    Re: Useing a 407C comp for R22 app?

    Thanks gents, ill do this tomorrow morning and report back!

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Useing a 407C comp for R22 app?

    Only difference in compressor made for R22 and for R407C is in filled oil. R407C compressor is filed with POE oil.
    In fact, there is no compressor made specifically for R407C. R407C is transition refrigerant made to be compatible with equipment made for R22.
    R22 is miscible with POE and mineral oil and you don't need to do anything except change compresor and filter dryer to one which is also compatible with POE oils and flush system with dry nitrogen from residual mineral oil left in pockets.

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Useing a 407C comp for R22 app?

    The only important thing that you have to look at is the oil type and compressor displacement.

Similar Threads

  1. hot cylinder york comp
    By jase in space in forum Trouble Shooting
    Replies: 13
    Last Post: 04-09-2010, 09:08 PM
  2. R22 TEV suitable to use on a 407c charge?
    By danielt_smith in forum Trouble Shooting
    Replies: 9
    Last Post: 19-11-2008, 02:12 PM
  3. Third comp change in three years, why?
    By expat in forum Commercial
    Replies: 44
    Last Post: 16-10-2008, 03:48 PM
  4. 2 Stage Comp Defrosting
    By jwasir in forum Fundamentals
    Replies: 0
    Last Post: 27-08-2008, 09:10 PM
  5. comp oil
    By headgasket in forum Technical Discussions
    Replies: 2
    Last Post: 14-10-2007, 07:34 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •