    Refrigerant R22/R404A



    Hi to all

    We normaly use Maneurop compressors, on this compressor
    we can change the oil and let them run on R404A instead of
    R22.
    Does anyone know if this is possible with. Lùnite compressors.
    The compressor is a Lùnite CAJ 9513 / R22

    Best regards
    Carlo Hansen



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Refrigerant R22/R404A

    We have done it anyway but removing the oil of a UH is not that easy. Be carefull when turning upside down that compressor doesn't comes out of his inner suspension springs.

    We even have applications where a R134a is running on R404a and vice versa but this was for special reasons.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Refrigerant R22/R404A

    Quote Originally Posted by Carlo Hansen
    Hi to all

    We normaly use Maneurop compressors, on this compressor
    we can change the oil and let them run on R404A instead of
    R22.
    Does anyone know if this is possible with. Lùnite compressors.
    The compressor is a Lùnite CAJ 9513 / R22

    Best regards
    Carlo Hansen
    Hello Carlo.

    I once ordered a hermitique condensing unit on R22.The supplier told me that they were temporarily out of stock, But they had the equivelant unit on r 404a.

    He then informed me that they were the same unit except one had mineral oil and the other synthetic.

    Purchased the r404a unit and ran it on r22.No problems.

  4. #4
    Join Date
    Mar 2005
    Location
    Belgium
    Age
    58
    Posts
    110
    Rep Power
    20

    Re: Refrigerant R22/R404A

    Quote Originally Posted by Carlo Hansen
    We normaly use Maneurop compressors, on this compressor
    we can change the oil and let them run on R404A instead of
    R22.
    Dear Carlo,
    Just to inform you: you should not do this on a regular basis.
    Maneurop states that "..Lifetime reduction shall be expected.." (what ever it means) when using R404A in a R22 compressor (with ester oil).
    There are some (minor) differences between the MTZ (for R404A) and MT (for R22) compressors like : other piston rings, stainless steel valves, ...

  5. #5
    Join Date
    Mar 2004
    Location
    Denmark
    Posts
    65
    Rep Power
    21

    Re: Refrigerant R22/R404A

    Hi again

    Thanks for the info. A have changed the oil and now a will see
    how long the system will be running.

    Best regards
    Carlo Hansen

Similar Threads

  1. R600 Refrigerant.
    By tonydeith in forum Refrigerants
    Replies: 14
    Last Post: 21-04-2011, 08:52 AM
  2. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  3. Replies: 2
    Last Post: 16-11-2005, 05:34 PM
  4. Liquid refrigerant and bubles in sightglass
    By aygul in forum Trouble Shooting
    Replies: 2
    Last Post: 30-08-2003, 09:07 PM
  5. Refrigerant Reclamation
    By herefishy in forum Commercial
    Replies: 6
    Last Post: 23-07-2003, 08:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •