    halo, can someone guide me to start my project...

    - i need 600 liter chilled water per hour
    - evaporator inlet water temp 37c
    - evaporator outlet water temp 15c

    thanks...
    and what is the different between refrigeration capacity and cooling capacity??
    Last edited by ah fai; 30-10-2010 at 06:43 AM.



  2. #2
    Join Date
    Oct 2010
    Location
    Monterrey, Mexico
    Age
    47
    Posts
    13
    Rep Power
    0

    Re: chiller capacity formula & calculation...

    2.47 TR u can close to 3TR

    How...

    TR=(GPM*(Temp in - Temp out))/24

    Its quik form to calculate a chiller capacity.

    Best regards

  3. #3
    Join Date
    May 2008
    Location
    malaysia
    Age
    40
    Posts
    82
    Rep Power
    16

    Re: chiller capacity formula & calculation...

    3TR mean chiller cooling capacity right? how about comppressor size?

    best regrads

  4. #4
    Join Date
    Oct 2010
    Location
    Monterrey, Mexico
    Age
    47
    Posts
    13
    Rep Power
    0

    Re: chiller capacity formula & calculation...

    hi, ah fai.

    ohh..... yes
    1 TR = 12,000BTU
    3 TR or RT = 36,000BTU
    u can use a tipical air condition compressor for R22 or R410 system.

  5. #5
    Join Date
    May 2008
    Location
    malaysia
    Age
    40
    Posts
    82
    Rep Power
    16

    Re: chiller capacity formula & calculation...

    thanks you so much friend...
    i think i will go for bitzer

  6. #6
    Join Date
    May 2008
    Location
    malaysia
    Age
    40
    Posts
    82
    Rep Power
    16

    Re: chiller capacity formula & calculation...

    halo paco..
    for select the condenser, expension device and evaporator, its depends on total cooling capacity??
    any formula???
    and what does it mean by compressor output m3/min?? for example bitzer.
    Last edited by ah fai; 02-11-2010 at 06:53 AM.

  7. #7
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    894
    Rep Power
    19

    Re: chiller capacity formula & calculation...

    Hi there,

    First of all lets use SI units.

    Q = M x Cp X DT

    Q = Capacity in kW
    M = Liquid mass flow rate kg/s
    Cp = Liquid specific heat kJ/kg.K
    DT = Liquid temperature difference °C

    Your mass flow rate is 0.166 kg/s

    Q = 0.166 x 4.18 x (37-15) = 15.2 kW

    You have to select a compressor which can give you 15.2 kW capacity at =3°C evaporating and 50°C condensing (if air cooled)

    NOW in actual life you can not have 37°C input water into the chiller all the time.
    Normal water chiller when starts, the entering water is warm say 35°C but after a little while the temperature goes down and chiller works perfectly.

    If entering temperature into the chiller is warm all the time then entering refrigerant will evaporate very quickly and suction pressure will be high.
    IOW your chiller will not work correctly.
    Normal chiller is designed for 12°C to 7°C.
    Cheers
    Even Einstein Asked Questions

  8. #8
    Join Date
    May 2008
    Location
    malaysia
    Age
    40
    Posts
    82
    Rep Power
    16

    Re: chiller capacity formula & calculation...

    thanks for ur help, im new to RE... how about condenser and evaporator???

  9. #9
    Join Date
    Jul 2010
    Location
    fiji islands
    Age
    68
    Posts
    14
    Rep Power
    0

    Re: chiller capacity formula & calculation...

    Firstly you need to find out the total heat load calculation, then you would able to size up chilled water shell and condenser and compressor from an engineering technical data.

  10. #10
    Join Date
    Jun 2010
    Location
    Africa
    Posts
    28
    Rep Power
    0

    Re: chiller capacity formula & calculation...

    Hi all:
    what is GPM, I want 2 use this formula

  11. #11
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: chiller capacity formula & calculation...

    GPM is gallons per minute. Imperial units. Anyway, for Ah fai, I don' think you will be able to find a suitable DX evaporator for 22K delta T. You will need to split the cooling at least twice or more, .

  12. #12
    Join Date
    Jan 2011
    Location
    denmark
    Age
    64
    Posts
    32
    Rep Power
    0

    Re: chiller capacity formula & calculation...

    Hi Lana
    When u say that normally a chiller is designed to function between temperature range of 12 celsius-7 celsius..what do u mean by that?..is it the relantionship between chilled-medium ind and chilled
    medium out of evaporator?..or?......pardon me this dumb question, but i´m experiencing problems on interpretation as well......best regards

  13. #13
    Ezekiel21's Avatar
    Ezekiel21 Guest

    Re: chiller capacity formula & calculation...

    anyone can give me a layout of a chiller system w/ auto refill of water using pressure tank.

  14. #14
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    400
    Rep Power
    18

    Re: chiller capacity formula & calculation...

    condenser capacity = evaporator capacity in kw + kw rating of the compressor motor

Similar Threads

  1. capacity calculation
    By steve thailand in forum Fundamentals
    Replies: 8
    Last Post: 25-10-2010, 01:42 AM
  2. Perfomance test for chiller units ~300 Ton capacity
    By sithayathulla in forum Air Conditioning
    Replies: 0
    Last Post: 15-08-2010, 06:26 PM
  3. York Chiller Capacity
    By albertdarkness in forum Commercial
    Replies: 0
    Last Post: 23-10-2009, 02:43 AM
  4. PHE chiller capacity
    By fassi in forum NH3
    Replies: 5
    Last Post: 17-04-2007, 03:33 AM
  5. Capacity calculation
    By Peter_1 in forum Fundamentals
    Replies: 15
    Last Post: 02-07-2006, 11:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •