    setting suction pressure



    Hi guys, i am currently working with a 3hp hitachi condensing unit, bohn let 120 evaporator and, danfoss ts2 TXV. currently i am getting 25psig (r404) suction pressure. I want it to go down to 20 psig (r404) suction pressure. how do i attain this? do i have to adjust the expansion valve?



  2. #2
    Join Date
    Nov 2009
    Location
    Western PA
    Age
    48
    Posts
    69
    Rep Power
    15

    Re: setting suction pressure

    Is the box at temperature?

    If not, wait until it is very close to temperature before adjusting anything.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: setting suction pressure

    Is the TXV correctly sized?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: setting suction pressure

    The suction pressure is not something to be set. It will be whatever it needs to be given the current conditions.

    Why do you want it to be 20psig?

  5. #5
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: setting suction pressure

    you do not set the suction pressure you set the super heat at the tev

  6. #6
    Join Date
    Apr 2010
    Location
    Australia
    Posts
    11
    Rep Power
    0

    Re: setting suction pressure

    Quote Originally Posted by chadng View Post
    Hi guys, i am currently working with a 3hp hitachi condensing unit, bohn let 120 evaporator and, danfoss ts2 TXV. currently i am getting 25psig (r404) suction pressure. I want it to go down to 20 psig (r404) suction pressure. how do i attain this? do i have to adjust the expansion valve?
    You don't set the suction pressure as previously stated, the suction pressure will vary depending on the load. If your superheat is set right the evap coil is doing all it can. Maybe you have other problems with this system. If you have all other temps/pressures etc and what you are trying to obtain temp. wise we can assist further. good luck

Similar Threads

  1. what is useful of Economizer?
    By Ahmed.ragab in forum Industrial Compressors
    Replies: 33
    Last Post: 18-08-2010, 12:15 PM
  2. york 5 ton ac low suction line pressure
    By greenhornBC in forum Air Conditioning
    Replies: 0
    Last Post: 29-01-2010, 03:55 AM
  3. suction pressure regulation
    By chillyblue in forum Commercial
    Replies: 15
    Last Post: 26-04-2008, 05:53 PM
  4. Cycle Stops at Low Suction Pressure
    By verstep in forum History of Refrigeration
    Replies: 6
    Last Post: 30-10-2007, 11:05 PM
  5. propane compressor suction drum
    By Ahmed_LNG in forum Refrigerants
    Replies: 7
    Last Post: 01-01-2006, 08:01 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •