    copeland oil level issue



    I have a problem with oil dissapearing out of the sight glass at start and run, but when the compressor shuts off the level comes back to the top of the sight glass within minutes. Compressor is 3 months old, freezer temp setpoint -32deg celsius, 5 other units all run ok, oil levels stay in sight glass, compressor pumps down and holds ok, no broken valves, compressor pulls temperature well, no change after hot gas defrost level still the same, unit does not have an oil seperator, I believe if oil was being pumped out the level would not appear in sight glass right after shut down, I suspect something internal but don't know what. all Ideas greatly appreciated.



  2. #2
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: copeland oil level issue

    Hi there,


    Are the compressors connected in parallel? OR is there standby compressor in the circuit (which is connected in parallel)?
    Even Einstein Asked Questions

  3. #3
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    19

    Re: copeland oil level issue

    probable reasons
    1) low load on evaporator whereby oil return velocity is low .
    2) pressure difference between suction line & crankcase ( this suggests suction filter in compressor partiallly blocked).
    4) if accumulator is provided , the hole in U tube bigger in size or blocked .When the compressor is off, the suction pressure build up in accumulator pushes oil throgh it .
    5) If the compressors are in parallel , oil level regulator or oil& gas balancing line valves needed ; if not provided .
    6) Check oil viscosity usually 46 to 55 is suggested .

    IN APPLICATIONS LIKE THIS , OIL SEPARATOR IS REQUIRED , SO IS ACCUMULATOR .

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: copeland oil level issue

    Superheat might be too low.

  5. #5
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: copeland oil level issue

    The problem is why only happens on that on if all the compressors are working on the same manifold?
    To make progress is never good enough, I want to do better and better and better

  6. #6
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: copeland oil level issue

    Maybe the piston rings or the oil scrapper rings are worn.
    To make progress is never good enough, I want to do better and better and better

  7. #7
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: copeland oil level issue

    Does the crankcase of that compressor is hotter than the ones of other compressors?
    To make progress is never good enough, I want to do better and better and better

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: copeland oil level issue

    If the compressor is stand-alone, I suspect frost on the suction strainer. When frost thaws, oil drips into the crankcase.

  9. #9
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: copeland oil level issue

    Quote Originally Posted by danod View Post
    I have a problem with oil dissapearing out of the sight glass at start and run, but when the compressor shuts off the level comes back to the top of the sight glass within minutes. Compressor is 3 months old, freezer temp setpoint -32deg celsius, 5 other units all run ok, oil levels stay in sight glass, compressor pumps down and holds ok, no broken valves, compressor pulls temperature well, no change after hot gas defrost level still the same, unit does not have an oil seperator, I believe if oil was being pumped out the level would not appear in sight glass right after shut down, I suspect something internal but don't know what. all Ideas greatly appreciated.

    I don't think you mentioned the refrigerant type??
    But at -35 the back pressure will be low..
    I would initialy look to the oil float on the side of the comp (assuming it has one) and then failing that
    if the condition persists look at the comp itself.

    You do not state what type of comp it is??
    But we are assuming that it is a semihermetic. If it is a scroll
    the fault could be very differant to a semi.

    If it is a semi and if the oil float is ok (swap it for one off another comp),
    then I would look to the comp itself. You may need to strip it down and check the valves and pistons.

    If it is only 3 months old, is it a rebuild? or brand new? does it have a warentee?

    taz

    .
    Last edited by taz24; 27-10-2010 at 04:08 PM.

  10. #10
    Join Date
    Nov 2008
    Location
    alberta canada
    Posts
    27
    Rep Power
    0

    Re: copeland oil level issue

    I should have been more specific. there are 3 separate freezers, each with 2 compressors
    and there own condensing units and evaporators. refrigerant is 404a. this compressor will pull the room temp down with no problem even with the 2nd compressor in defrost. It will pull down to 10hg vacumm no problem and hold for a pump down test. The compressor is a copeland 3db, was new from Copeland in 2008, sat on the shelf for a spare until July this year when it replaced one with broken connecting rod, probably a slug of oil. The last contractor installed a 2nd suction accumulator in series on both compressors for this particular freezer because of smashed comp's.

  11. #11
    Join Date
    Nov 2009
    Location
    Western PA
    Age
    48
    Posts
    69
    Rep Power
    15

    Re: copeland oil level issue

    Quote Originally Posted by danod View Post
    I should have been more specific. there are 3 separate freezers, each with 2 compressors
    and there own condensing units and evaporators. refrigerant is 404a. this compressor will pull the room temp down with no problem even with the 2nd compressor in defrost. It will pull down to 10hg vacumm no problem and hold for a pump down test. The compressor is a copeland 3db, was new from Copeland in 2008, sat on the shelf for a spare until July this year when it replaced one with broken connecting rod, probably a slug of oil. The last contractor installed a 2nd suction accumulator in series on both compressors for this particular freezer because of smashed comp's.


    Hmmm.

    The word 'Probably' is rarely a good one when dealing with diagnosing the cause of failure for a compressor.

    Was is a slug of oil or a slug of liquid refrigerant?

    I'll bet that, if you are able to answer this question, you will find the thread that unravels your larger problem.

    2 Suction accumulators in series is crazy as far as I'm concerned. Either install a properly sized accumulator or resolve the problem that is creating the liquid floodback condition that necessitates the accumulator to begin with.


    If presented with a problem like this, I would start with a logging device and log temperatures, pressures and other data I felt pertinent to the problem based on the exact equipment on-site. After a period of time, you will be able to establish baseline performance and see when things deviate from the baseline. Once you know WHEN things are deviating from the baseline, then you will be able to investigate WHY they are.

  12. #12
    Join Date
    Nov 2008
    Location
    alberta canada
    Posts
    27
    Rep Power
    0

    Re: copeland oil level issue

    jpsmith 1cm, I know 'probably' isn't the correct way of diagnosing a problem. I only used that word based on my observations of a rising ice level on the first suction accumulator over a couple of days. If you saw what I observed you would Probably agree that an oil slug took out the last comp. Based on my observations on the first game the Giants will Probably win the series.

  13. #13
    Join Date
    Nov 2008
    Location
    alberta canada
    Posts
    27
    Rep Power
    0

    Smile Re: copeland oil level issue

    found the problem to the dissapearing oil level. turned out the factory remanufactured compressor was missing the bearing on the motor end on the crank, all the oil would get pumped into that end

  14. #14
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: copeland oil level issue

    Quote Originally Posted by danod View Post
    found the problem to the dissapearing oil level. turned out the factory remanufactured compressor was missing the bearing on the motor end on the crank, all the oil would get pumped into that end
    Impressive carelessness from Copeland.

  15. #15
    phil2424's Avatar
    phil2424 Guest

    Re: copeland oil level issue

    Copeland do not remanufacture compressors - I think Danod is saying an independent compressor rebuilder Messed up

  16. #16
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: copeland oil level issue

    how it could be .
    carter is lower than motor side and between there is a bearing (it is check valve ) from motor side to carter side

  17. #17
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: copeland oil level issue

    Why were there broken rods before? Has the cause been remedied?

    Broken rods on refrigerant cooled Copeland's from "slugging" can only happen if the compressor suffers flooded-starts - not flood-backs.

    http://fridgetech.com/articles/recipfailmodes/#GlossB

    Rods can also break from flood-backs on refrigerant cooled compressors but you would see heatless white metal smearing along the journals (big end) and especially the main motor-end bearing.

    http://fridgetech.com/articles/recipfailmodes/#GlossA
    Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.

Similar Threads

  1. R290 Suction Scrubber HI Level
    By Knappyfro in forum Trouble Shooting
    Replies: 1
    Last Post: 28-11-2009, 05:15 PM
  2. "Unstable" Rack Receiver Liquid Level
    By chweber in forum Commercial
    Replies: 3
    Last Post: 09-02-2009, 08:58 AM
  3. Risk in high compressor oil level?
    By Ice Queen in forum Trouble Shooting
    Replies: 0
    Last Post: 20-05-2008, 02:28 PM
  4. Replies: 4
    Last Post: 18-12-2007, 06:42 AM
  5. Oil level control question
    By racknovice in forum Supermarket Refrigeration
    Replies: 1
    Last Post: 06-09-2007, 09:29 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •