    410a service port size regulations



    Hi. Does anyone know if it is illegal to sell a 410A Heat Pump with 1/4 service/gauge ports, in the UK. Looked though all my Fgas Stuff and cant find any info on this. Cheers



  2. #2
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: 410a service port size regulations

    I don't know, but if it has 1/4" instead of 3/8" schraders, the system will enable the standard 1/4" guages to be connected to it. As the 410a guage connections are always 3/8".

    Case scenario.

    Keeping the standard 1/4" schraders on the system would be like wiring a 13 amp socket to 415 volts, and putting a notice on it saying 415volts only. How many people do you think would still plug in everyday appliances in there? Change it to 3/8" schraders, and maintain the expected standard.

    You never know, the next time you connect your standard 1/4" guage lines to a unit, it might be 410a inside there with a small and dirty label displaying 410a. And it could be painful.

    Have you checked the chemical companies safe use and guidance of 410a. I'm sure I've either seen a BS number or a Suva guidance note about the schraders being 3/8" for 410a.

  3. #3
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: 410a service port size regulations

    Quick correction there as R410a service schraders are 5/16 flare

  4. #4
    Join Date
    Aug 2008
    Location
    ENGLAND
    Age
    54
    Posts
    27
    Rep Power
    0

    Re: 410a service port size regulations

    Hi Thanks. I know all about 410A, and the problems occurred if you connect standard gauges etc. due to pressures/cross contamination etc. and that is why we have seperate gauges.
    I had a meeting yesterday with an American company and they use the same gauges for R407C as for 410A. So they must have the same gauge port size. They are thinking of selling in the UK. But they would come with 1/4 gauge ports. Hence the question.

  5. #5
    Join Date
    Nov 2009
    Location
    Western PA
    Age
    48
    Posts
    69
    Rep Power
    15

    Re: 410a service port size regulations

    In the USA, R410 units are available with standard 1/4" schraeders.

    While it would be nice to have different sized ports to deter use of the wrong gauges, it would also be a pain in the neck to have to run back to the truck to get the correct fittings/hoses/manifold to service the equipment.

  6. #6
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: 410a service port size regulations

    Quote Originally Posted by jpsmith1cm View Post
    In the USA, R410 units are available with standard 1/4" schraeders.

    While it would be nice to have different sized ports to deter use of the wrong gauges, it would also be a pain in the neck to have to run back to the truck to get the correct fittings/hoses/manifold to service the equipment.
    Hey JP

    Is that you from the other forum. We need your experience on here. How you doing anyway? good I hope.

  7. #7
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: 410a service port size regulations

    Quote Originally Posted by Quality View Post
    Quick correction there as R410a service schraders are 5/16 flare
    Thats what I meant to say .

    I've only ever worked with it a few times. And I just borrowed the 410a gauges from a friend. I just noticed the hoses and the schraders were slightly bigger than 1/4". And to be honest I would have thought by now that they would have been standardised to 5/16."

    They've looked into all the other factors and overlooked the obvious one .

  8. #8
    Join Date
    Nov 2009
    Location
    Western PA
    Age
    48
    Posts
    69
    Rep Power
    15

    Re: 410a service port size regulations

    Quote Originally Posted by chilliwilly View Post
    Hey JP

    Is that you from the other forum. We need your experience on here. How you doing anyway? good I hope.

    Yes, the one and (hopefully) only JP.

    I hang out here occcasionally, but the topics of discussion tend to range a bit away from my area of expertise so I generally refrain from commenting unless I KNOW something.


    There are some VERY smart dudes that hang out here.

    WE in the states could use a few like these guys. Knock our refer mechanics about a little. Rough 'em up and make them realize that simply posessing a gauge manifold does NOT make one a professional technician or engineer, which I actually prefer but has a different connotation on this side of the pond.

  9. #9
    Join Date
    Aug 2008
    Location
    ENGLAND
    Age
    54
    Posts
    27
    Rep Power
    0

    Re: 410a service port size regulations

    We have to carry seperate sets of gauges for the different gasses. 1 for R22 etc. with 1/4 schrader and and 1 for 410a with 5/16 schrader. This is mainly to stop cross contamination of the different oils used and to stop someone connecting up their standard gauges with a maximum suction gauge pressure of 150 PSI to a 410a system and blowing them up with the higher pressures.

  10. #10
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: 410a service port size regulations

    .


    Quote Originally Posted by CHIZEL010 View Post

    Hi. Does anyone know if it is illegal to sell a 410A Heat Pump with 1/4 service/gauge ports, in the UK. Looked though all my Fgas Stuff and cant find any info on this. Cheers


    Not sure about the legal part of it, but going back a few years (quite a few, actually) to when R410A was first touted as an alternative to the alternatives at the time that were replacing R22, the one thing that was apparent, that gave a lot of safety concerns was the much higher opperating pressures that you get with R410A:
    It was recognised that the safe opperating pressures for much of the range of service equipment available at the time, (gauges, manifolds and the like) would be exceeded to the point where they may be unsafe.

    It was this point that prompted many of the Japanese manufacturers at the time to design in a larger service port to exclude service gauges designed for R22, R407C and the like that were not safely designed for the higher pressures.

    So, if you can demonstrate that your manifolds and gauge sets are equal to or exceed the Maximum Allowable Pressues for the sytem they are attached to, it doesn't matter what size the gauge ports are.

    In the EU the standards to read to understand pressure safety are EN 378 and the Pressure Equipment Directive if the equipment is covered by it.
    I think that this would have been covered in your F Gas work.

    So, the law, to my knowledge, does not specifically pronounce on what sizes you should use, but it is a requirement of sale that the equipment is safe and further as an expert, you are aware of the safety issues.



    .
    Last edited by Argus; 28-10-2010 at 03:34 PM.

  11. #11
    Join Date
    Nov 2009
    Location
    Western PA
    Age
    48
    Posts
    69
    Rep Power
    15

    Re: 410a service port size regulations

    Quote Originally Posted by CHIZEL010 View Post
    We have to carry seperate sets of gauges for the different gasses. 1 for R22 etc. with 1/4 schrader and and 1 for 410a with 5/16 schrader. This is mainly to stop cross contamination of the different oils used and to stop someone connecting up their standard gauges with a maximum suction gauge pressure of 150 PSI to a 410a system and blowing them up with the higher pressures.

    I have always thought that the oil cross contamination issue to be very much over-blown.

    The amount of oil that would be transferred by a service manifold set during normal service work is minimal.

  12. #12
    Join Date
    Aug 2008
    Location
    ENGLAND
    Age
    54
    Posts
    27
    Rep Power
    0

    Re: 410a service port size regulations

    Thanks all. Pretty much as I thought. But trying to get an exact answer from anyone is not easy. They make these governing bodies who you have to pay to be registered with and you get no straight answers, is that because they dont know and we are all wasting our money. I agree this trade should be regulated to stop the cowboys, but help the people who are trying to do everything correctly, with some better info.

  13. #13
    Join Date
    Feb 2009
    Location
    Australia
    Posts
    272
    Rep Power
    16

    Re: 410a service port size regulations

    I don't know any fridgy who doesn't have 2 sets of guages,,,,,one for 410 and one for the rest.

  14. #14
    Join Date
    Dec 2004
    Location
    U.K
    Age
    55
    Posts
    518
    Rep Power
    21

    Re: 410a service port size regulations

    Quote Originally Posted by lawrence1 View Post
    I don't know any fridgy who doesn't have 2 sets of guages,,,,,one for 410 and one for the rest.
    At the very least?

Similar Threads

  1. Service Partners Required
    By Mike Woods in forum Commercial
    Replies: 0
    Last Post: 01-09-2010, 09:50 AM
  2. Vauxhall Opel Zafira High Side Service port Query
    By Nomolos in forum Technical Discussions
    Replies: 7
    Last Post: 06-07-2010, 11:05 PM
  3. Dupont line size calculator also has 410a and 407c
    By 128cyclist in forum Tools and Calculators
    Replies: 6
    Last Post: 20-08-2009, 03:45 PM
  4. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM
  5. Balanced port TEVs
    By Prof Sporlan in forum Fundamentals
    Replies: 22
    Last Post: 25-02-2002, 03:43 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •