Required temperature output from chiller is not obtained
Vapor compressor chilled brine plant:
30 TR capacity, -25 C is the required output
Problem: Temperature is not going beyond -14 C
Brine: 50% - MEOH + 50% - Water
SPG: 0.93
Refrigerant: Ammonia
Chiller Type: Shell & Tube, 6 pass
Compressor Discharge Pressure: 12 kg/cm2
Compressor Suction Pressure: 0.15 kg/cm2
Difference in Temperature around chiller: 1.5 C
Chiller Area is 45 m2
-
25-10-2010, 01:44 PM #2
Re: Required temperature output from chiller is not obtained
heat load excessive or cooling capacity insufficient.
-
25-10-2010, 01:56 PM #3
Re: Required temperature output from chiller is not obtained
No excessive heat load because it is under recirculation mode from tank to chiller to tank. Cooling capacity is sufficient because liquid ammonia from condenser is at 38 C
-
25-10-2010, 02:39 PM #4
Re: Required temperature output from chiller is not obtained
Cooling capacity is sufficient because liquid ammonia from condenser is at 38 C[/quote]
Huh? I am not an ammonia guy but this dosnt seem to make sense, someone please explain
-
25-10-2010, 06:17 PM #5
Re: Required temperature output from chiller is not obtained
Both concept don't make sense at all.
No excessive heat load because it is under recirculation mode from tank to chiller to tank
Cooling capacity is sufficient because liquid ammonia from condenser is at 38 C
Similar Threads
-
Condensor split temperature
By Peter_1 in forum FundamentalsReplies: 14Last Post: 31-07-2011, 05:49 PM -
This a long one - AKV
By Peter_1 in forum IndustrialReplies: 6Last Post: 26-12-2008, 11:47 AM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM -
Article in ACH&R News
By Gary in forum FundamentalsReplies: 8Last Post: 20-05-2003, 12:27 AM -
TEV with MOP: how to keep valve body temp above bulb temp?
By DaBit in forum FundamentalsReplies: 5Last Post: 16-10-2002, 12:38 AM