Evap above compressor - changing compressor type
I have an application in a very small system, where the evaporator is located above a rotary compressor, with integral suction accumulator. The system contains a capillary tube expansion device.
I would like to change the compressor to a hermetic, refrigerator-type, which does not have a suction accumulator. My concern is how to manage potential liquid flood-back from the evaporator & droplet carryover.
I have looked into small suction line accumulators, but these are very difficult to find, at the capacity of the system under consideration. Space is also at a premium.
I'd appreciate advice & applied wisdom on how to achieve this system change in a safe manner, with maximum compressor protection afforded. Thanks so much for your help.
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
25-10-2010, 06:18 AM #2
Re: Evap above compressor - changing compressor type
Most rotaries have a SA mounted on it because they could be used widely an many times in reversible systems. But, SA's are not always needed.
I thought that many manufactures have a table where you can read max charge a compressor in a cap system may have.
The sump of a hermetic compressor can hold also some refrigerant.
I don't see much troubles with not adding one.
In the worst case, you always can add a small crankcase heater and make sure you have an oil siphon after the evaporator so that liquid can't flow back.
If it was me, I shouldn't worry to much and leave the SA. What's the new compressor model and refrigerant charge?
Or you can always find a small SA in many small domestic freezers on the scrapyard.
I'm sure, all things you certainly knew but hadn't think about it or you just needed a confirmation of your ideas.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
25-10-2010, 07:30 AM #3
Re: Evap above compressor - changing compressor type
Thanks so much Peter.
Peter_1:
If it was me, I shouldn't worry to much and leave the SA. What's the new compressor model and refrigerant charge?
I'm sure, all things you certainly knew but hadn't think about it or you just needed a confirmation of your ideas.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
25-10-2010, 08:57 AM #4
Re: Evap above compressor - changing compressor type
http://www.ra.danfoss.com/TechnicalI...3_Cd44p402.pdf
SC12G,n max charge, 1300 grams, so no problem at all.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
25-10-2010, 09:39 AM #5
Re: Evap above compressor - changing compressor type
^ Thanks so much, Peter. I always like to quadruple-check everything before cutting metal.
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
25-10-2010, 11:44 AM #6
Re: Evap above compressor - changing compressor type
Also if there is possibility stop with pump-down...
In some places will have to think ...
Similar Threads
-
Bad Evap?
By Telecaster1 in forum CommercialReplies: 6Last Post: 07-09-2010, 12:34 AM -
Oil distrubution problem with a evap, how to fix?
By Henry. in forum FundamentalsReplies: 3Last Post: 06-07-2010, 04:35 PM -
iced up evap coil
By wilks in forum FundamentalsReplies: 6Last Post: 31-08-2007, 09:15 PM -
how to wire in pause before evap fan kicks in after defrost ?
By knighty in forum ElectricalReplies: 10Last Post: 21-01-2007, 01:08 AM -
Evap motor no come on
By Apprentice in forum Technical DiscussionsReplies: 13Last Post: 04-12-2003, 04:07 PM