    Evap above compressor - changing compressor type



    I have an application in a very small system, where the evaporator is located above a rotary compressor, with integral suction accumulator. The system contains a capillary tube expansion device.

    I would like to change the compressor to a hermetic, refrigerator-type, which does not have a suction accumulator. My concern is how to manage potential liquid flood-back from the evaporator & droplet carryover.

    I have looked into small suction line accumulators, but these are very difficult to find, at the capacity of the system under consideration. Space is also at a premium.

    I'd appreciate advice & applied wisdom on how to achieve this system change in a safe manner, with maximum compressor protection afforded. Thanks so much for your help.


    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Evap above compressor - changing compressor type

    Most rotaries have a SA mounted on it because they could be used widely an many times in reversible systems. But, SA's are not always needed.

    I thought that many manufactures have a table where you can read max charge a compressor in a cap system may have.
    The sump of a hermetic compressor can hold also some refrigerant.

    I don't see much troubles with not adding one.
    In the worst case, you always can add a small crankcase heater and make sure you have an oil siphon after the evaporator so that liquid can't flow back.

    If it was me, I shouldn't worry to much and leave the SA. What's the new compressor model and refrigerant charge?

    Or you can always find a small SA in many small domestic freezers on the scrapyard.

    I'm sure, all things you certainly knew but hadn't think about it or you just needed a confirmation of your ideas.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Evap above compressor - changing compressor type

    Thanks so much Peter.

    Peter_1:
    If it was me, I shouldn't worry to much and leave the SA. What's the new compressor model and refrigerant charge?
    An example here would be the Danfoss SC12G, with max refrigerant charge of 1.3kg. The final system charge will be around 600g, or less.

    I'm sure, all things you certainly knew but hadn't think about it or you just needed a confirmation of your ideas.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Evap above compressor - changing compressor type

    http://www.ra.danfoss.com/TechnicalI...3_Cd44p402.pdf

    SC12G,n max charge, 1300 grams, so no problem at all.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Evap above compressor - changing compressor type

    ^ Thanks so much, Peter. I always like to quadruple-check everything before cutting metal.

    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  6. #6
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Evap above compressor - changing compressor type

    Also if there is possibility stop with pump-down...
    In some places will have to think ...

Similar Threads

  1. Bad Evap?
    By Telecaster1 in forum Commercial
    Replies: 6
    Last Post: 07-09-2010, 12:34 AM
  2. Oil distrubution problem with a evap, how to fix?
    By Henry. in forum Fundamentals
    Replies: 3
    Last Post: 06-07-2010, 04:35 PM
  3. iced up evap coil
    By wilks in forum Fundamentals
    Replies: 6
    Last Post: 31-08-2007, 09:15 PM
  4. Replies: 10
    Last Post: 21-01-2007, 02:08 AM
  5. Evap motor no come on
    By Apprentice in forum Technical Discussions
    Replies: 13
    Last Post: 04-12-2003, 05:07 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •