    I have an application in a very small system, where the evaporator is located above a rotary compressor, with integral suction accumulator. The system contains a capillary tube expansion device.
    I would like to change the compressor to a hermetic, refrigerator-type, which does not have a suction accumulator. My concern is how to manage potential liquid flood-back from the evaporator & droplet carryover.
    I have looked into small suction line accumulators, but these are very difficult to find, at the capacity of the system under consideration. Space is also at a premium.
    I'd appreciate advice & applied wisdom on how to achieve this system change in a safe manner, with maximum compressor protection afforded. Thanks so much for your help.
    Oct 2003
    5,630
    Re: Evap above compressor - changing compressor type
    Most rotaries have a SA mounted on it because they could be used widely an many times in reversible systems. But, SA's are not always needed.
    I thought that many manufactures have a table where you can read max charge a compressor in a cap system may have.
    The sump of a hermetic compressor can hold also some refrigerant.
    I don't see much troubles with not adding one.
    In the worst case, you always can add a small crankcase heater and make sure you have an oil siphon after the evaporator so that liquid can't flow back.
    If it was me, I shouldn't worry to much and leave the SA. What's the new compressor model and refrigerant charge?
    Or you can always find a small SA in many small domestic freezers on the scrapyard.
    I'm sure, all things you certainly knew but hadn't think about it or you just needed a confirmation of your ideas.
    Mar 2009
    KZN, South Africa
    64
    2,212
    Thanks so much Peter.
    Peter_1:
    An example here would be the Danfoss SC12G, with max refrigerant charge of 1.3kg. The final system charge will be around 600g, or less.
    Oct 2003
    5,630
    http://www.ra.danfoss.com/TechnicalI...3_Cd44p402.pdf
    SC12G,n max charge, 1300 grams, so no problem at all.
    Mar 2009
    KZN, South Africa
    64
    2,212
    ^ Thanks so much, Peter. I always like to quadruple-check everything before cutting metal.
    Nov 2009
    Minsk, Belarus
    171
    Also if there is possibility stop with pump-down...
    In some places will have to think ...
  1. Bad Evap?
    By Telecaster1 in forum Commercial
    Last Post: 07-09-2010, 12:34 AM
  2. Oil distrubution problem with a evap, how to fix?
    By Henry. in forum Fundamentals
    Last Post: 06-07-2010, 04:35 PM
  3. iced up evap coil
    By wilks in forum Fundamentals
    Last Post: 31-08-2007, 09:15 PM
  4. Replies: 10
    Last Post: 21-01-2007, 01:08 AM
  5. Evap motor no come on
    By Apprentice in forum Technical Discussions
    Last Post: 04-12-2003, 04:07 PM