24-10-2010, 11:55 PM #1
I have recently purchased a model 4MXS32GVJU outdoor unit and 2 CTX509GVJU and 1 FTXS15DVJU indoor units. I am very happy with the operation as a whole,however I am less than happy with the controls. Is there a way to operate one indoor unit on "heat" and another unit on "fan" or "dry"? It would seem to me that this makes sense and on A/C I am able to run a fan on one unit and A/C on another.Also,on A/C,the fan runs continuously,as I would like it to do on heat,rather that start and stop with the heat cycle. I have contacted my installer and he tells me that there is no way to do this. When I try to do this the louvers on the unit on heat or dry open but nothing happens.
Any thoughts please?
25-10-2010, 10:33 PM #2
Re: Daikin multi split controls
The units donīt operate the fan all the time during heating to stop cold drafts and keep the coil temperature up. Every heat pump does this (or should) and it is a good thing.
You canīt have one unit on heat and one on dry because dry is basically cooling with a really slow fan (itīs a bit more complicated then that) and it is not possible for the system to heat and cool at the same time.
Not sure about the fan only thing, never tried to do that. I would think that it should be possible, I canīt see a reason why not.
26-10-2010, 12:22 AM #3
Thanks airefresco, what you say makes perfect sense, I didn't realize that dry was just kind of a slow cool,and it makes sense concerning the fan on continuously with the heat as well.
I appreciate your thought,thanks again.
02-11-2010, 03:13 PM #4
I have a 2MXS50G at my parents house and I'm 99% sure you can't have 1 fan coil on heat and the other on fan only as the hot gas still gets pumped around both indoors although the other indoor is switched off.
04-11-2010, 08:12 AM #5
04-11-2010, 01:43 PM #6
06-11-2010, 02:18 AM #7
It isnt possible to have fan mode on when another indoor is in heating, these units have common discharge header on outdoor before tee of to indoors .
06-11-2010, 02:49 AM #8
06-11-2010, 04:10 PM #9
06-11-2010, 07:09 PM #10
07-11-2010, 04:06 PM #11
I am 100% positive that in cooling mode you can have one in fan only and the other in cool.
The fan only will not cool as the eev will shut down,
In heat mode what stops the unit from heating on thermo off if the compressor is still running for another circuit? The eev shuts down to stop the refigerant going though the coil otherwise you would never stop heating or cooling.
07-11-2010, 05:21 PM #12
Thats correct in cooling the EEV shuts down completly so you can have units in fan mode or cooling mode but in heating any units that are thermo off or turned off will have the EEVs open approx 10% to assist with oil return back to the compressor.
So yes you are correct in cooling mode but in heating mode small ammount of refrigerant continues to circulate all units. Its upto the control logic to ensure that the fan does not run so as heating doesnt continue.
On my crappy LG system the fan cycles on and off periodically on the floor mounted units to clear build up of heat from the coil however due to poor control strategy the fan stays on too long and the room over heats!
My wall mounted units dont run the fan at all at thermo off even though the coil will still be warm due to circulating refrigerant.
08-11-2010, 07:51 PM #13
Same logic as vrv then, as the eev,s stay open 10% in heatnig
17-11-2010, 01:43 AM #14
I've been away for a bit and not able to keep up with the forum. There is a wealth of information here, Thanks to all who responded.
Old Daikin Multi system, help please!
By ArisL in forum Trouble ShootingReplies: 4Last Post: 19-07-2010, 07:10 PM -
Mitsi City Multi VS Daikin VRV
By sumsor in forum FundamentalsReplies: 5Last Post: 14-07-2010, 05:54 PM -
Daikin twin split trouble
By dave ldms in forum Air ConditioningReplies: 1Last Post: 25-02-2010, 07:34 PM -
fujitsu multi split, how it works??
By 123-steve909 in forum Air ConditioningReplies: 9Last Post: 04-06-2009, 07:07 AM -
Daikin Multi Split A/C problems
By timholmes204 in forum Air ConditioningReplies: 6Last Post: 22-05-2008, 12:09 AM