    Installation query - Ceiling Mounted Evaporators



    Please can somebody advise me as to what the industry "norm" is for fixings on ceiling mounted evaporators? I recently became involved in a case whereby a newly installed evaporator (single fan approx 25kg) came loose from it's fixings inside a walk in freezer. The installer had used 4 x .75inch self-tapping screws to ceiling mount. The freezer is standard design - aluminium skin, insulation and then outer skin.

    I thought the suggested fixing method was studding?



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Installation query - Ceiling Mounted Evaporators

    We use special bolts that holds the evaporator firmly to the ceiling.
    Attached Images Attached Images

  3. #3
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Installation query - Ceiling Mounted Evaporators

    Best practice: nylon threaded rod

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Installation query - Ceiling Mounted Evaporators

    Generally i like to use either nylon threaded rod on small evaporators and stainless steel on big ones. Something to keep in mind is it needs to be able to hold the evaporator up if it becomes full of ice which could be anything from a few kilos to a few tons.

    One of the companies i subbie for has wooden beams built in to the roof panel where the evaporator is going to be sited and uses coach screws. This is because there is often no access to the roof to fit rods in the small shops he specialises in.

    It would also be worth checking the manufactures recommendations.

    Jon

  5. #5
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Installation query - Ceiling Mounted Evaporators

    Nylon studding as Mr B and Monkey suggest.

    The nylon is used to alleviate hygiene and corrosion issues I believe. Using 4" screws eh? Well depending on the thickness of insulation the screws may only have gone through 1 skin. If they went through both then best not kneel on the top fixings unless your name is Officer Murphy. Doubt if the coldroom skin is designed (thick enough) to hold that weight anyway. Bad job.

    Cheers,

    Andy
    Health and safety first..........unless I'm in a hurry.

  6. #6
    sighmon55's Avatar
    sighmon55 Guest

    Re: Installation query - Ceiling Mounted Evaporators

    Does anybody know where/if there is any "industry guidelines" on this type of install?

  7. #7
    sighmon55's Avatar
    sighmon55 Guest

    Re: Installation query - Ceiling Mounted Evaporators

    I presume this method involves drilling through from topside all the way into the freezer - Certainly seems a secure method equivalent to standard studding.

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Installation query - Ceiling Mounted Evaporators

    Drilling through the panels will give you cold-bridges.
    If you tighten firmly a bolt-through evaporator, you will have a small crater on the roof of the freezer (under the bolt/washer)where the condensed water will collect.
    Therefore, the nylon threads like Richard proposed solves this problem.
    We mostly slide a small piece of Armaflex over the bolts and glue it.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    sighmon55's Avatar
    sighmon55 Guest

    Re: Installation query - Ceiling Mounted Evaporators

    Going back to the original query - I presume using small (.75 inch) self-tappers in this case is a no no?

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Installation query - Ceiling Mounted Evaporators

    The original installer must attach his units in such a way that they under normal conditions can't fall from the ceiling, whatever method he wants to use for this.
    In your case, the evaporator fas fallen from the ceiling under normal conditions, so he failed to accomplish standard, safe requirements.
    If this should be a case for The Court, then I should take the install instructions of the manufacturer, measure the predrilled holes in the evaporator, and try to find how much load you can hang on a screw.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Installation query - Ceiling Mounted Evaporators

    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  12. #12
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Installation query - Ceiling Mounted Evaporators

    Hello Gents

    In my case I use stainless steel treaded rod up through the ceiling to cross beams suspended from the main building structure, with aramaflex sealed over the rods with silicone.
    Small rooms can have the coolers supported by unistrut run above the room wall to wall with treaded rod dropped down through the ceiling. If you space the unistrut off the ceiling panel you can add some armaflex to the rod to stop cold bridging or sweating.

    Screws unless stainless rust and break, ceiling panels have no support normally for you to fix anything to

    Kind Regards Andy D
    If you can't fix it leave it that no one else will:rolleyes:

  13. #13
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Installation query - Ceiling Mounted Evaporators

    i use 100mm square plates under the nut and washer with a liberal coating of silicone under the plate and around the threaded rod.good vapour seal and stronger support
    mmm to beer or not to beer...........lets drink breakfast

Similar Threads

  1. B& Q airforce ceiling mounted corner unit
    By bossblue in forum Air Conditioning
    Replies: 6
    Last Post: 25-07-2010, 04:54 PM
  2. ceiling mounted remote control for split A/C units
    By stevethebungee in forum Air Conditioning
    Replies: 1
    Last Post: 27-04-2010, 09:01 PM
  3. Hitachi Ceiling Mounted Indoor Unit Defect
    By Daikin=Overated in forum Air Conditioning
    Replies: 2
    Last Post: 06-11-2007, 08:49 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •