    capacity calculation



    hi, does anyone know what cooling capacity i need to cool a liquid (beer in my case) from 10degC to 2degC if the flow rate is 10liters/minute?

    we are using a heat exchanger to cool the beer in line as it goes to the filling machine. i need to buy a chiller to drive the heat exchanger and need to know the capacity for it.

    thanks, steve



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: capacity calculation

    To cool that beer from 10°-2°C with that flow, you need cca 6kW/h energy removed from beer.

    Q=m*c*(T2-T1)

    Q= Energy in Wh
    m= mass (cca 600kg in one hour)
    c=specific heat capacity of beer (water) (cca 1,16 Wh/(kg*K))
    T2-T1= temperature diferential (in your case 10°C-2°C=8K)

    Capacity of chiller than would be cca 6kW.
    Last edited by nike123; 22-10-2010 at 09:00 AM.

  3. #3
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: capacity calculation

    @Steve. If you are in Thailand, pm me & I'll give you a useful falang RHVAC manufacturer to talk to.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  4. #4
    Join Date
    Mar 2010
    Location
    thailand
    Age
    65
    Posts
    13
    Rep Power
    0

    Re: capacity calculation

    thanks, so i have another idea. it turns out a chiller and heat exchanger is a bit outside of my budget right now, basically like here to the moon outside my budget so i have another idea.

    i have a plastic ice chest, i plan to fill it with ice and water, so water temp about 1-2degC.

    i will make a stainless steel box (heat exchanger) , 40cm high, 80cm long, 2-3mm wide (inside). i will drill many 1/2" holes between the two walls and weld 1/2" stainless tube through. so this is my heat exchanger, surface area about 0.5m3, liquid thickness 2mm.

    beer comes in at the bottom corner and out the top diagonally opposite corner. flow rate is the same as my original post, 20L/min and beer temp going in is about 8degC.

    what temperature drop can i expect to get in this setup? I am aiming to get down to about 3-4 degrees so i wonder, will one of these heat exchangers do it or will i need a few?

    by the way, i know i will need to replace the ice a lot as it melts. that's ok, large ice blocks here are quite cheap and i can use the melt water for something else in the bottle filling process (bottle washer/chiller).

    thanks again, steve

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: capacity calculation

    In original post you have 10/l min of beer. Now it is 20. Which is correct?

  6. #6
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: capacity calculation

    Get a PHE from AlfaLaval, in BKK.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  7. #7
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: capacity calculation

    beer comes in at the bottom corner and out the top diagonally opposite corner.
    For best heat transfer it should flow the other way - from up to down.

  8. #8
    Join Date
    Mar 2010
    Location
    thailand
    Age
    65
    Posts
    13
    Rep Power
    0

    Re: capacity calculation

    Quote Originally Posted by nike123 View Post
    In original post you have 10/l min of beer. Now it is 20. Which is correct?
    my mistake on original post, it is 20L/min

    what is a PHE? i'll look into it

    moving the beer from bottom to top makes it easier to bleed air from the system on startup i think

    thanks

  9. #9
    Join Date
    Mar 2010
    Location
    thailand
    Age
    65
    Posts
    13
    Rep Power
    0

    Re: capacity calculation

    Quote Originally Posted by desA View Post
    Get a PHE from AlfaLaval, in BKK.
    oh, Plate Heat Exchanger

    i will when i have money, for now i need to make up my own using ice as a coolant

Similar Threads

  1. Replies: 3
    Last Post: 29-04-2010, 10:30 AM
  2. Replies: 30
    Last Post: 25-04-2010, 12:40 PM
  3. Capacity Calculation for Deep Freeze cold store
    By Asheesh in forum Technical Speculations
    Replies: 3
    Last Post: 08-08-2009, 09:40 AM
  4. How to increase pool heater capacity?
    By Drew in forum Commercial
    Replies: 104
    Last Post: 13-06-2009, 05:25 AM
  5. Capacity calculation
    By Peter_1 in forum Fundamentals
    Replies: 15
    Last Post: 02-07-2006, 11:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •