    Over feeding TEV



    Hello everyone,

    If a TEV is overfeeding liquid into the evaporator due to bad bulb mounting or broken valve the result would be little or no superheat. Now with this (if i have read correctly) also comes lack of cooling.?

    is this statement above correct? if so, is the lack of cooling because the refrigerant isnt changing state (latent heat) thus isnt gaining enough heat from the "refrigerated space?"

    really im asking for a small explanation on the reasoning for the lack of cooling even though there is "too much" liquid refrigerant in the evap, so much infact that it marches out of the evap and into the comp, Doh! :/

    I thank anyone in advance as any info is greatly appreciated and soaked up by my "eager to learn brain", lol
    Last edited by SkyWalker; 20-10-2010 at 08:54 PM.



  2. #2
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Over feeding TEV

    Hi Skywalker, the lack of cooling is the result of insufficient pressure difference from high to low side, so firing refrigerant unchecked into the evaporator will flood it but without the significant pressure drop to boil off liquid refrigerant, your liquid will walk right on through and find something else to do like damage the compressor..mike.

  3. #3
    Join Date
    Nov 2006
    Location
    At home
    Posts
    181
    Rep Power
    18

    Re: Over feeding TEV

    thanks for that mike, makes sense

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Over feeding TEV

    Quote Originally Posted by SkyWalker;207216...

    If a TEV is overfeeding liquid into the evaporator due to bad bulb mounting or broken valve the result would be little or no superheat. Now with this (if i have read correctly) also comes lack of cooling.?....
    Decreasing SH will increase evaporator capacity because more surface is used to use the effect from the change of state of the liquid. All surface taken to superheat is lost evaporator capacity.
    Second, overfeeding will increase LP of compressor, so better compression efficiency and lower compression ratio (=higher COP).
    Last edited by Peter_1; 24-10-2010 at 12:26 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. How do you ?
    By overscore23 in forum Technical Discussions
    Replies: 7
    Last Post: 01-08-2010, 12:52 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •